Sorry, for the wrong heading for the original post.

The building is a laboratory. So there are hazardous substances. I still
need to check what gets collected in the pit. The maintenance guy told me it
is for storing rain water.

Assuming it is rain water (till I check it out) would this pit have to be
sprinklered? If it is for containment of spills of chemicals, would it have
to be sprinklered then?

Tony 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bruce Verhei
Sent: April 20, 2012 5:03 PM
To: [email protected]
Subject: Re: Water testing volumes

Tony

Are there hazardous materials in the building?  Is this "secondary
containment" per IFC/IBC?

Bruce

Sent from my Motorola ATRIXT 4G on AT&T

-----Original message-----
From: Ron Greenman <[email protected]>
To: [email protected]
Sent: Fri, Apr 20, 2012 21:06:59 GMT+00:00
Subject: Re: Water testing volumes

Tony,

You just described open grate flooring. See NFPA 13/2010 8.5.5.3.1. Note
that nothing is said about what's under the grated floor being relevant.
Earlier versions have, if not exact, similar language.

On Fri, Apr 20, 2012 at 12:26 PM, A.P.Silva <[email protected]> wrote:

>
> In an industrial building there is a concrete storage tank below gound 
> level. It is about 19'x7' and 10 feet deep and covered with an open 
> grated steel panel. Top of the steel panel is level with the adjacent 
> ground floor level. Someone said it was to collect rain water but I 
> need to get that confirmed. It could even be that the other floor 
> drains drained into this tank and was pumped out. Anyway, this space 
> is non-combustible, but could collect debris that would fall through 
> the open grate panel. The question is, does it have to be sprinklered? 
> I would say NO, but is there anything in the code to justify that 
> position?
>
> Tony
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120420/c64c113e/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120420/05a52655/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to