If it's for rainwater what's the hazard you'd be protecting?  Would you protect 
a retention pond?  Not trying to be snarky but just trying to post some 
parallels for thought.

It's outside, non-combustible, so no, I wouldn't propose any type of internal 
sprinklers.  Now if it was right up against a building and it would contain 
appreciable amounts of non-diluted combustible or flammable chemicals due to a 
spill within the building there may be cause to look at some exposure 
protection for the building but that would take a lot more information and 
analysis.

We've used this approach on many projects where secondary containment was 
required

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Tuesday, April 24, 2012 2:10 AM
To: [email protected]
Subject: RE: Storage pit

 
Sorry, for the wrong heading for the original post.

The building is a laboratory. So there are hazardous substances. I still
need to check what gets collected in the pit. The maintenance guy told me it
is for storing rain water.

Assuming it is rain water (till I check it out) would this pit have to be
sprinklered? If it is for containment of spills of chemicals, would it have
to be sprinklered then?

Tony 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bruce Verhei
Sent: April 20, 2012 5:03 PM
To: [email protected]
Subject: Re: Water testing volumes

Tony

Are there hazardous materials in the building?  Is this "secondary
containment" per IFC/IBC?

Bruce

Sent from my Motorola ATRIXT 4G on AT&T

-----Original message-----
From: Ron Greenman <[email protected]>
To: [email protected]
Sent: Fri, Apr 20, 2012 21:06:59 GMT+00:00
Subject: Re: Water testing volumes

Tony,

You just described open grate flooring. See NFPA 13/2010 8.5.5.3.1. Note
that nothing is said about what's under the grated floor being relevant.
Earlier versions have, if not exact, similar language.

On Fri, Apr 20, 2012 at 12:26 PM, A.P.Silva <[email protected]> wrote:

>
> In an industrial building there is a concrete storage tank below gound 
> level. It is about 19'x7' and 10 feet deep and covered with an open 
> grated steel panel. Top of the steel panel is level with the adjacent 
> ground floor level. Someone said it was to collect rain water but I 
> need to get that confirmed. It could even be that the other floor 
> drains drained into this tank and was pumped out. Anyway, this space 
> is non-combustible, but could collect debris that would fall through 
> the open grate panel. The question is, does it have to be sprinklered? 
> I would say NO, but is there anything in the code to justify that 
> position?
>
> Tony
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120420/c64c113e/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120420/05a52655/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to