The only time I have seen that be an issue, is when it was a fire rated wall or 
partition. The fire caulk manufacturer can't provide a listed detail that 
includes a fitting. If the engineer is looking at the future accessibility of 
the fitting, well, it would be no different if it was located within floor 
trusses or above a drywall ceiling. The only NFPA requirement is that valves be 
in an accessible location. Fittings are installed within inaccessible locations 
every day. 


Thanks,
Eric Tysinger CET
NICET III - 108988
Designer/Project Manager - Fort Myers Branch
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Fort Myers, Florida 33905
p: (239)433-3030 x1240    f: (239)433-3263
C: (239)633-9703



-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Craig Leadbetter
Sent: Thursday, April 26, 2012 2:15 PM
To: sprinklerforum@firesprinkler.org
Subject: Mechanical fitting in wall

We have a situation where a vic coupling was covered by a wall/soffit for 
aesthetics. The engineer is questioning whether a vic coupling can be in a wall 
that is not a chase. I am looking for input.

Thanks

--
Craig Leadbetter
Safeguard of Marquette
PO Box 116
Marquette, MI 49855

(O) 906-475-9955
(F) 906-475-5474
(C) 906-362-5393

craigleadbet...@gmail.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120426/3546bf46/attachment.html>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to