Had an old thought challenged and I think I have learned something. Situation:

High rise building with a fire pump. Churn plus static to provide 100 psi 
(discharge side of most demanding hose valve) on combined standpipe creates 
just over 200 psi on bottom floor. Instantly I think to use pressure regulating 
valve for the lower systems,  feed lower systems before pump boost or run a 
secondary standpipe. Another estimator tells me that most sprinkler components 
are rated for well over 175. I didn't believe it but looking at several 
products from several manufacturers seems to prove him right. There were a few 
exceptions such as some sprinkler heads and hose valves but for the pipe, 
fittings, valves etc there was no problem. If the project was FM it would be 
tougher as most of the standard 5.6 heads were 250 UL but 175 FM.

NFPA 13 2007 6.1.3 System components shall be rated for the maximum system 
working pressure to which they are exposed but shall not be rated at less than 
175 psi for components installed above ground..."

Am I missing something here or does over pressurization of the lower floor only 
require pressure reducing hose valves and not system prv's as long as the 
components are rated for more than the  "... maximum system working pressure to 
which they are exposed..." which seems to be the case for the vast majority of 
components.



[Description: LOGO_10]
Rod DiBona
Vice President
Rapid Fire Protection
office : (605)348-2342
fax : (605)348-0108
cell : (605)391-3553
www.rapidfireinc.com<http://www.rapidfireinc.com>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120517/8f1261f3/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 6561 bytes
Desc: image001.jpg
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120517/8f1261f3/attachment.jpg>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to