I tried to make the same case with an engineering firm who was reviewing my
plans and they insisted on OH. Seeing how noncombustible porte-cocheres
aren't required to be sprinkled at all it would only make sense that if the
construction does require them to be sprinkled then it would be light
hazard - either way it's not considered "automobile parking" since the
vehicles are transient. I think you can make a case from the code for LH.



On Fri, May 18, 2012 at 12:24 PM, Bob <[email protected]> wrote:

> Forum,
> Hope everybody's day is going well.  With a drive thru Porte cohere is the
> density light hazard or OH1?  13 says that the cars should not be
> considered
> storage, that being the case there is no storage beneath.  Light hazard
> would seem appropriate at this point.
>
> Thanks,
>
> Bob Knight, CET III
> 208-318-3057
> www.firebyknight.com
>
>
>
>