If you're going to put sprinklers beneath what are they going to be protecting? 
  What density would you use for automobile parking?

OH1 would be suitable since it lines up with the recommendation for hazards in 
NFPA 13.  2007-A.5.3.1.

Light hazard wouldn't be worth running the pipe.  If there was something to 
catch fire there what would it be, most likely it would be a vehicle so protect 
appropriately.



Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bob
Sent: Friday, May 18, 2012 3:24 PM
To: [email protected]
Subject: Porte Cohere Density

Forum,
Hope everybody's day is going well.  With a drive thru Porte cohere is the
density light hazard or OH1?  13 says that the cars should not be considered
storage, that being the case there is no storage beneath.  Light hazard
would seem appropriate at this point.

Thanks,

Bob Knight, CET III
208-318-3057
www.firebyknight.com