If you're going to put sprinklers beneath what are they going to be protecting? What density would you use for automobile parking?
OH1 would be suitable since it lines up with the recommendation for hazards in NFPA 13. 2007-A.5.3.1. Light hazard wouldn't be worth running the pipe. If there was something to catch fire there what would it be, most likely it would be a vehicle so protect appropriately. Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SCĀ 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bob Sent: Friday, May 18, 2012 3:24 PM To: [email protected] Subject: Porte Cohere Density Forum, Hope everybody's day is going well. With a drive thru Porte cohere is the density light hazard or OH1? 13 says that the cars should not be considered storage, that being the case there is no storage beneath. Light hazard would seem appropriate at this point. Thanks, Bob Knight, CET III 208-318-3057 www.firebyknight.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum