:) Thanks George,

I'll try to clarify briefly:
This whole thread is simply a tweak to "my proposal", and it has been
misunderstood by some due to my colorful miss-use of English. I want to tie
density to sprinkler height and area to occupancy: Area LH=1000, OHI=1500,
OHII=2000, density .008 gpm/s.f. times sprinkler height in feet. This is
what I have come to realize from some limited modeling I've done so far, and
it gets rid of the QR Reduction at 20' glitch. It is the reason I said I
think the demands are too high for low ceilings and too low for high
ceilings. I am not sure about the actual testing phase of the whole process,
but I am not advocating any new products. (And when the head pops, we
usually have far more than 7 psi Pt on it). Thanks again George,
Brad 

-----Original Message-----
From: George Church [mailto:[email protected]] 
Sent: Monday, June 04, 2012 3:10 PM
To: [email protected]
Subject: RE: 7psi Minimums for Fire Sprinklers

You DO understand the cost of the path ahead of you, especially when you're
trying to get fire tests done?
There is a large item you may have missed:
Economic feasibility
Since I'd guess there is but a small number of these sprinklers that would
be sold in a year.

Various manufacturers have their own little "Edsels" that they invested R&D
$ into, but aren't getting the return for them.
Even when times are good, they are prudent about what they invest in, and
I'm not certain that saving a couple PSI is one of them.

If they have enough water to make the plumbing work, they've got 7 PSI up to
a certain flow. But for the cost required to get the listing done and the
sprinkler on the market, you'd prolly need a quantum change in the min EHP,
not 2 PSI. It would look better as a % saved (save 28% of your EHP!) but
when it comes right down to it, its 20% of what we generally leave as a
throwaway cushion.

I have had a lot of ideas I scrapped quickly because of the risk/reward
economic viability measure. At one time, folks were putting up bar joists
with the chords made of pipe so we could connect and use them as our
sprinkler system, I believe in the 80's. Obviously, that idea's time hasn't
come (yet). We see very few commercial multipurpose systems, despite what
appears at first to be great cost savings.

I keep a pad of paper and a pencil in the drawer of my nightstand. I don't
remember the last time I awoke with an idea great enough to write down, but
maybe I just sleep better than I used to. Or I've grown to appreciate
rolling over and going back to sleep.


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to