Jockey pump stop pressure seems reasonable.
Scott Mitchell

Ralphy Henderson <[email protected]> wrote:

>I have an existing system fed by an existing fire pump requiring an expansion 
>chamber (by the local AHJ) for a small a/f system. I'm a little confused on 
>how to size this when it comes to 'operating pressure'. In the past we sized 
>it based upon the city static pressure. In this case the fire pump is 
>oversized and has a PRV sitting at 150 psi. Would the expansion chamber need 
>to be sized based upon 150 psi 'operating pressure' or am I missing something?
>
>Thanks,