I think your asking if it is acceptable to convert an existing pipe schedule with standard response sprinklers to quick response sprinklers. Although you aren't required too change them since it is existing, if I were you AND the sprinklers were going to be changed anyways, I'd go that route.

Good question since the schedule was defined using the SR sprinklers. Lets start with 13:22.5.1.2 (2010 ed) which only restricts the k- factor, not the thermal response. To put your mind at ease in case you were thinking that it could mean that the TC just has been asked or thought about this issue, read on. Unlike storage (where we have a faster growing, more challenging fire that could cause too many sprinklers to open), LH or OH would only benefit from a faster response (as shown by the same density but smaller area for all spray sprinklers).

Roland

NFPA required caveat that this is my opinion and not that of NFPA or any of its technical committees.


On Jul 2, 2012, at 8:14 AM, Todd - FPDC wrote:

I am recommending replacing all of the sprinklers on a pipe schedule system in a school. SR or QR heads?