> Date: Mon, 2 Jul 2012 17:38:38 -0400
> To: [email protected]
> From: [email protected]
> Subject: Re: Head replacement on pipe sched
> 
> This is a dry system installed in 1899. The current sprinklers are from 1954 
> (+/-) and are being replaced due to age. FWIW, we did an internal inspection 
> and are going to do a full flushing as well. 
> 
> 
> 
> At 03:19 PM 7/2/2012, you wrote:
> >I think your asking if it is acceptable to convert an existing pipe 
> >schedule with standard response sprinklers to quick response 
> >sprinklers. Although you aren't required too change them since it is 
> >existing, if I were you AND the sprinklers were going to be changed 
> >anyways, I'd go that route.
> >
> >Good question since the schedule was defined using the SR sprinklers. 
> >Lets start with 13:22.5.1.2 (2010 ed) which only restricts the k- factor, 
> >not the thermal response. To put your mind at ease in case 
> >you were thinking that it could mean that the TC just has been asked 
> >or thought about this issue, read on. Unlike storage (where we have 
> >a faster growing, more challenging fire that could cause too many 
> >sprinklers to open), LH or OH would only benefit from a faster 
> >response (as shown by the same density but smaller area for all spray 
> >sprinklers).
> >
> >Roland
> >
> >NFPA required caveat that this is my opinion and not that of NFPA or 
> >any of its technical committees.
> >
> >
> >On Jul 2, 2012, at 8:14 AM, Todd - FPDC wrote:
> >
> >>I am recommending replacing all of the sprinklers on a pipe schedule 
> >>system in a school. SR or QR heads?
> >>
> >>Sent from my iPhone
> >>_______________________________________________
> >>Sprinklerforum mailing list
> >>[email protected]
> >>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
                                          
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120703/a48ed701/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to