How would you interpolate if there is only one density for a 16.8K sprinkler?

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: [email protected] [mailto:[email protected]] 
Sent: Monday, August 27, 2012 1:29 PM
To: [email protected]
Subject: Idle wood pallets NFPA 13, 12.12.1.2(a) 2010 Ed

I posted this two weeks ago and no one bit so I thought I would try again. I 
know we can interpolate densities based on area etc... but is it okay to 
interpolate storage height based on density when only a single point is given 
in the table? We have and area/density system that is capable of 0.495/2000 
using 16.8K heads. Interpolating between 0.60 for 20 ft. storage and 0.495 
would allow 16'-6" max storage height of idle pallets.

Ron Fletcher
Aero - Phoenix