Look at table 12.12.1.2(a), 2010. The minimum density is .60 from 8ft to 20 ft. The .45 is only good to 8 ft. Unless the pile sizes are small and well spaced I think you are looking at 8-10 ft max height. The orifice size at 11.2 and above is not the most important factor. The density controls heat.
Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Monday, August 27, 2012 1:29 PM To: [email protected] Subject: Idle wood pallets NFPA 13, 12.12.1.2(a) 2010 Ed I posted this two weeks ago and no one bit so I thought I would try again. I know we can interpolate densities based on area etc... but is it okay to interpolate storage height based on density when only a single point is given in the table? We have and area/density system that is capable of 0.495/2000 using 16.8K heads. Interpolating between 0.60 for 20 ft. storage and 0.495 would allow 16'-6" max storage height of idle pallets. Ron Fletcher Aero - Phoenix _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum ----- No virus found in this message. Checked by AVG - www.avg.com Version: 2012.0.2197 / Virus Database: 2437/5227 - Release Date: 08/27/12 ----- No virus found in this message. Checked by AVG - www.avg.com Version: 2012.0.2197 / Virus Database: 2437/5227 - Release Date: 08/27/12 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum