Look at table 12.12.1.2(a), 2010. The minimum density is .60 from 8ft to 20
ft. The .45 is only good to 8 ft. Unless the pile sizes are small and well
spaced I think you are looking at 8-10 ft max height. The orifice size at
11.2 and above is not the most important factor. The density controls heat.


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Monday, August 27, 2012 1:29 PM
To: [email protected]
Subject: Idle wood pallets NFPA 13, 12.12.1.2(a) 2010 Ed

I posted this two weeks ago and no one bit so I thought I would try again. I
know we can interpolate densities based on area etc... but is it okay to
interpolate storage height based on density when only a single point is
given in the table? We have and area/density system that is capable of
0.495/2000 using 16.8K heads. Interpolating between 0.60 for 20 ft. storage
and 0.495 would allow 16'-6" max storage height of idle pallets.

Ron Fletcher
Aero - Phoenix

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum



-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2197 / Virus Database: 2437/5227 - Release Date: 08/27/12

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2197 / Virus Database: 2437/5227 - Release Date: 08/27/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to