Looking over a job where the EOR wants to use cylinders to supply the air for a 
dry system.  There is plenty of power to the building so that's not the issue.  
They are showing lab air cylinders from both air (NC) and nitrogen (NO) into an 
AMD into the system.  I get automatic air is not required.  But I'm seeing NFPA 
13 '12-7.2.6.5.1 limiting air supply when AUTOMATIC to dependable shop system 
or a compressor.  I don't see bottles being allowed.  Or that is to say I don't 
see bottles as being a dependable shop system.

I assume some of you have done bottles for the air to a dry system?  As I read 
you can have them if someone manually opens a valve and refills the system when 
needed?  Of course this is even confusing.  Is there something on a manual fill 
system that requires daily checking?  Or are they relying on the low pressure 
alarm to note when time to refill?  Actually, the low pressure alarm isn't even 
required, right, so are they waiting for a system trip to know when to add air?

If manual is allowed isn't an AMD off a bottle a little better but not quite 
the full blown compressor?  Why would they restrict the middle on the order of 
worst to best?

Who wants to straighten me out 'cuz none of us here have ever seen bottles used 
on a system?

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]<mailto:[email protected]>
www.burnsmcd.com<http://www.burnsmcd.com/>

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN




-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121004/0e12d424/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to