Most generators, if not all, have a nitrogen storage tank.  The one I used
put out 70 PSI requiring an AMD and we still had a riser mount air
compressor because the generator could not fill in 30 minutes.  They're
interconnected and valved.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Thursday, October 04, 2012 5:44 PM
To: [email protected]
Subject: Re: Air Supply

If you use nitrogen (7.6.2.7)  it now kicks you over to 7.2.6.5 (Automatic
Air Maintenance).  Must admit, I see no reason to use an air tank and plenty
not to (as George already said).  I'd say an air cylinder would be not
different than a nitrogen cylinder when it comes to requiring an AMD.  If
you do not have a low pressure alarm, the pressure gauge has to be checked
weekly instead of monthly.  Now that dry pipe system have to have an air
leakage test performed every 3 years, there shouldn't be any systems (or at
least as many) needing a compressor running full time to keep it from
tripping.

Roland

On Oct 4, 2012, at 12:54 PM, Cahill, Christopher wrote:

> Looking over a job where the EOR wants to use cylinders to supply the 
> air for a dry system.  There is plenty of power to the building so 
> that's not the issue.  They are showing lab air cylinders from both 
> air (NC) and nitrogen (NO) into an AMD into the system.  I get 
> automatic air is not required.  But I'm seeing NFPA 13 '12-7.2.6.5.1 
> limiting air supply when AUTOMATIC to dependable shop system or a 
> compressor.  I don't see bottles being allowed.  Or that is to say I 
> don't see bottles as being a dependable shop system.
>
> I assume some of you have done bottles for the air to a dry system?   
> As I read you can have them if someone manually opens a valve and  
> refills the system when needed?  Of course this is even confusing.   
> Is there something on a manual fill system that requires daily 
> checking?  Or are they relying on the low pressure alarm to note when 
> time to refill?  Actually, the low pressure alarm isn't even required, 
> right, so are they waiting for a system trip to know when to add air?
>
> If manual is allowed isn't an AMD off a bottle a little better but not 
> quite the full blown compressor?  Why would they restrict the middle 
> on the order of worst to best?
>
> Who wants to straighten me out 'cuz none of us here have ever seen 
> bottles used on a system?
>
> Chris Cahill, PE*
> Senior Fire Protection Engineer, Aviation & Facilities Group Burns & 
> McDonnell
>
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to