Sorry, Matt beat me to the punch.

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Dewayne
Martinez
Sent: Monday, October 08, 2012 2:56 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: small rpz's

But are they listed UL for fire protection use?  Since the valves are
not "slow close" they may not be.  Our state reviewing agency made us
change to the new backflows that use a slow close valve, such as a
Milwaukee BB, instead of the models with ball valves only.  

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve
Leyton
Sent: Monday, October 08, 2012 2:43 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: small rpz's

AND, you can get a tamper switch kit for the ball valves if the system
is required to be supervised.


Steve Leyton




-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Richard
Carr
Sent: Monday, October 08, 2012 12:42 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: small rpz's

The smaller one are listed with the ball valves, use it as is or you
lose the listing.

Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
6555 Grace Lane.
Jacksonville, Fl. 32205
rc...@coxfire.com
904-781-8227


-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Greg
McGahan
Sent: Monday, October 08, 2012 3:23 PM
To: sprinklerforum@firesprinkler.org
Subject: small rpz's

I am just double checking myself here...

If you need an 1-1/4" rpz for an antifreeze loop - yes I know this is
probably the last one we will ever put in - do you have to get it with
OS&Y valves or can you sue the stack on the shelf model with the ball
valves?

Thanks,
Greg


--
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20121008/4cc93e21/attachment.html>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to