Thank you Craig.

Per 11.4.6.2 we plan on installing a sensor to determine when the tank is at
the two-thirds level and that sensor will be wired to the controller as
there is a receptor supplied. The owner wants to use this level as their low
level so they will maintain this much fuel at all times. 

Does this sound acceptable?

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax 
(731) 267-4853 cell
www.keyfireprotection.com
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Thursday, October 25, 2012 12:44 PM
To: [email protected]
Subject: RE: Diesel Tanks NFPA 20

Sight tubes cannot be used for determine fuel levels, (11.4.2.6.1) it must
be a monitored signal device.  With automatic run testing it could be months
before someone actually went into a pump room and looked at the sight tube
to see what the level is.  

11.4.2.4  says you need to provide a device that will provide a signal,

11.4.6.2 says at what level the device needs to alarm.

They go hand in hand.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Thursday, October 25, 2012 12:05 PM
To: [email protected]
Subject: RE: Diesel Tanks NFPA 20

One is a switch and the other can be a sight glass.

Ron Fletcher
Aero Phoenix

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Johnson,
Duane (NIH/OD/ORS) [C]
Sent: Thursday, October 25, 2012 9:01 AM
To: '[email protected]'
Subject: Re: Diesel Tanks NFPA 20

Need both. 

----- Original Message -----
From: Bobby Gillett [mailto:[email protected]]
Sent: Thursday, October 25, 2012 11:55 AM
To: [email protected] <[email protected]>
Subject: RE: Diesel Tanks NFPA 20

Any thoughts at all? 

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax 
(731) 267-4853 cell
www.keyfireprotection.com
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Thursday, October 25, 2012 9:28 AM
To: [email protected]
Subject: Diesel Tanks NFPA 20

I know this is an NFPA 20 question, but I am hoping to get clear on
something if anyone can help.

 

NFPA 20:

11.4.2.4 A means shall be provided in the tank for low fuel level signal
initiation.

11.4.2.6.2 A fuel level indicator shall be provided to activate at the
two-thirds tank level.

 

If I am correct, 11.4.2.6.2 is requiring an indicator to activate when the
tank is 1/3 below its capacity, and I assume that this is so they can
maintain a minimum amount of fuel at all times (if they react when
notified). Wouldn't this also act as the low fuel level signal that 11.4.2.4
is requiring? 

 

Thank you,

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <http://www.keyfireprotection.com> www.keyfireprotection.com

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20121025/8f8040ed/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2013.0.2741 / Virus Database: 2616/5851 - Release Date: 10/24/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2013.0.2741 / Virus Database: 2616/5851 - Release Date: 10/24/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to