the 8 sprinklers is only residential sprinklers.
8.15.6 Space Under Ground Floor - What would you call it other than a
crawl space? The 3000 does apply to the ground floor when sprinklers
are omitted from the crawl space as stated in 11.2.3.1.4(3).
Roland
On Oct 24, 2012, at 10:19 AM, Rod DiBona wrote:
I believe that the crawl space does meet the intent as long as it
meets the requirements on that section. I am going by memory but I
believe that there can't be any storage or fuel fired equipment and
maybe a couple of others. One key to this is that I believe that the
space above then has to use a 3,000 ft calc area. I think the 2013
is going to minimum of 8 heads (AFSA convention) in lieu of the
3,000 but for now it is 3,000.
Rod at Rapid