the 8 sprinklers is only residential sprinklers.

8.15.6 Space Under Ground Floor - What would you call it other than a crawl space? The 3000 does apply to the ground floor when sprinklers are omitted from the crawl space as stated in 11.2.3.1.4(3).

Roland


On Oct 24, 2012, at 10:19 AM, Rod DiBona wrote:

I believe that the crawl space does meet the intent as long as it meets the requirements on that section. I am going by memory but I believe that there can't be any storage or fuel fired equipment and maybe a couple of others. One key to this is that I believe that the space above then has to use a 3,000 ft calc area. I think the 2013 is going to minimum of 8 heads (AFSA convention) in lieu of the 3,000 but for now it is 3,000.

Rod at Rapid