On Sat, Nov 10, 2012 at 6:46 AM, Bill Brooks <bill.bro...@brooksfpe.com>wrote:

> I definitely don't agree with this. Pipe racks are routinely installed in
> industrial settings and are used for transiting roadways and other parts of
> industrial sites.  The piping on these racks is designed by folks who use
> standards other than NFPA 13.  I would recommend using the equivalency
> provisions of Section 1.5 in this case and allowing the piping
> professionals
> the ability to provide the calculations needed.  Sometimes we lose sight of
> this important provision.
>
> Bill Brooks
>
> William N. Brooks, P.E.
> Brooks Fire Protection Engineering Inc.
> 372 Wilett Drive
> Severna Park, MD 21146-1904
> 410-544-3620
> 410-544-3032 FAX
> 412-400-6528 Cell
>
>
> -----Original Message-----
> From: sprinklerforum-boun...@firesprinkler.org
> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
> craig.pr...@ch2m.com
> Sent: Thursday, November 08, 2012 10:31 AM
> To: sprinklerforum@firesprinkler.org
> Subject: RE: Pipe support spacing requirements for structural supports
>
> If the spacing of pipe rack supports does not meet the spacing requirements
> of the NFPA Standards you need to supplement with intermediate hangers in
> order to have a compliant installation.  I just don't use what's given.
>
> Craig L. Prahl, CET
> Fire Protection
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> craig.pr...@ch2m.com
>
>
>
> -----Original Message-----
> From: sprinklerforum-boun...@firesprinkler.org
> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
> rfletc...@aerofire.com
> Sent: Thursday, November 08, 2012 9:48 AM
> To: sprinklerforum@firesprinkler.org
> Subject: RE: Pipe support spacing requirements for structural supports
>
> I agree that you would have to follow NFPA 13/15 hanger requirements for
> spacing of pipe stands you are building to support pipe around like a pump
> set or a transformer. In the pipe rack however I think you can only use
> what
> you are given. In the past we have used flanges to join bulk pipes in the
> rack. Threaded branchlines hold up okay with hangers every 20 ft. Of course
> we did all of this back before the scientists got involved in NFPA 13 so if
> it was solid, wouldn't wiggle if pulled on, didn't fall down from its' own
> weight and didn't move when flow tested it was good enough.
>
> Ron Fletcher
> Aero -Phoenix
>
> -----Original Message-----
> From: sprinklerforum-boun...@firesprinkler.org
> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
> craig.pr...@ch2m.com
> Sent: Thursday, November 08, 2012 7:29 AM
> To: sprinklerforum@firesprinkler.org
> Subject: RE: Pipe support spacing requirements for structural supports
>
> Whether it's a pipe stand, a hanger or pipe rack, they must conform to the
> spacing requirements of the applicable standard.  NFPA 15(2012) 5.6 defers
> to NFPA 13 for hangers.  I can't find any A10.4.1 in NFPA 15, 2012.
>
> So no, 20' hanger spacing is not compliant with the NFPA 13 or NFPA 15
> standards.  The assertions of the structural engineer are incorrect.
>
> Additionally,  I would suggest looking at the installation manuals provided
> by the coupling manufacturers to see if they refer to any particular
> support
> spacing requirements if there is specific direction needed.
>
> Craig L. Prahl, CET
> Fire Protection
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> craig.pr...@ch2m.com
>
>
> -----Original Message-----
> From: sprinklerforum-boun...@firesprinkler.org
> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Hinson,
> Ryan
> Sent: Tuesday, November 06, 2012 7:07 PM
> To: sprinklerforum@firesprinkler.org
> Subject: Pipe support spacing requirements for structural supports
>
> I've got a couple projects which have pipe racks for supporting above grade
> firewater piping.  These rack supports are spaced at 20' or more on center.
> From the NFPA 13 Handbook at the beginning of Chapter 9, pipestands are to
> have the same safety factors as hangers.  NFPA 15 is suggested for
> additional guidance.  NFPA 13 limits hanger spacing to 15'.  NFPA 15 (2012)
> Sections 6.3.2.2 and 6.3.2.3 state that firewater piping shall be supported
> under fire conditions and shall be supported from steel or concrete
> structural members or pipestands.  "Do these also need to conform to the 15
> ft maximum spacing?"
>
> I've received this question from a structural engineer regarding the pipe
> support requirements for NFPA 13 (2010) Chapter 9.  His assertion is that
> this refers to pipe stand and pipe hanger spacing requirements for piping
> 8"
> and smaller only.  As such, his feeling is that there are no limits on
> spacing for concrete and steel support conditions other than those required
> per AWWA M11 4th Edition Chapter 7 and sound structural engineering design.
> Incidentally, NFPA 15 (2012) Section 6.3.2.2 calls out structural supports
> specifically as if there is some difference for their design and does not
> actually provide a limit.
>
> Both NFPA 20 (2010) Section 4.13.5 and NFPA 24 (2010) Section 12.1 state
> above ground piping and fittings must comply with NFPA 13 regarding hangers
> and supports.
>
> NFPA 15 Section A.10.4.1 refers to AWWA M11 as applicable for installation
> of pipe and fittings.
>
> NFPA 15 Table 6.3.2.2.2 only goes up to 8" pipe.  AWWA M11 has some pipe
> support requirements for steel piping.  At first glance, they do not appear
> applicable for fire water systems as they are not specifically included in
> Chapter 1 Uses.  Chapter 7, Supports for Pipe, states the load is
> determined
> to be the weight of the water filled pipe.  NFPA 13 requires the load to be
> 5 times the weight of the water filled pipe (see Section 9.1.1.2(1)).  The
> 5
> times load factor seems to be only applied to hangers and stands as well,
> applying this to steel and concrete supports would be too conservative.  It
> appears the design of the steel and concrete supports would be covered by
> AISC 13th edition, ASCE 7-05, and ACI 318 codes.
>
> As an example to the above difference:  See 8" Schedule 40 pipe (this is
> standard weight pipe).  The wall thickness is .322 inches.  Per AWWA M11
> Table 7.1, this approximately nominal 5/16" wall thickness can have
> supports
> 45 ft apart.  8" schedule 10 (3/16" wall thickness) can be spanned up to
> 38'
> according to this table!  I'm not up on the nuances of piping and
> deflection
> but I believe the intent is to provide considerable safety into the
> supports
> of all types for firewater related piping.
>
> Is it the opinion of the forum that 15' along with the allowable extensions
> per NFPA 15 is the maximum or are we to use structurally designed supports
> at their stated allowable spans for supporting this piping?  What say you?
>
> Ryan L. Hinson, EIT, SET
> Senior Fire Protection Engineer, Aviation & Facilities Group Burns &
> McDonnell Minneapolis-St. Paul Office
> 8201 Norman Center Drive, Suite 300
> Bloomington, MN 55437
> Direct: 952-656-3662
> Fax: 952-229-2923
> rhin...@burnsmcd.com
> www.burnsmcd.com<BLOCKED::www.burnsmcd.com>
>
>
> Proud recipient of PSMJ's Premier Award for Client Satisfaction
>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
> s/20121106/24d34187/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121110/5ad8d8a1/attachment.html>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to