No to your first question, Yes to your last. :-)

Remember 8.6.4.1.2 (3) requires you within 1"-12" of the ceiling/deck when
installed the way you describe. That measurement, coupled with the
dimension, seems to supersede any concerns of height vs. distance for
obstructions to me.

R/
Matt

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Gregg Fontes
Sent: Tuesday, December 11, 2012 5:58 PM
To: sprinklerforum@firesprinkler.org
Subject: I-BEAM Bottom Flange Obstruction

Scenario: multi level mezzanine, W12 x 19, 4'-6 o.c., bottom flange at 9'-0,
top of storage 8'-0.  To get the 18" clearance, need to be 6" above the
bottom flange centered in the 4'-6 dimension.  There will be a line of
sprinklers in each 4'-6 I-beam pocket.  Do I need to be concern with the 4"
wide bottom flange if spaced on both sides?  I can not meet Table 8.6.5.1.2
and meet the 18" clearance.  However, 8.6.5.1.2 (2) states sprinklers are
permitted on opposite sides of obstructions not exceeding 4' in width
provide you do not exceed sprinkler spacing.  Since the sprinklers lines
would be 4'-6 o.c. I am o.k. there, so can I ignore the 4" bottom flange
since I can not spray under it?    

Thanks,
Gregg Fontes