No to your first question, Yes to your last. :-) Remember 8.6.4.1.2 (3) requires you within 1"-12" of the ceiling/deck when installed the way you describe. That measurement, coupled with the dimension, seems to supersede any concerns of height vs. distance for obstructions to me.
R/ Matt -----Original Message----- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Gregg Fontes Sent: Tuesday, December 11, 2012 5:58 PM To: sprinklerforum@firesprinkler.org Subject: I-BEAM Bottom Flange Obstruction Scenario: multi level mezzanine, W12 x 19, 4'-6 o.c., bottom flange at 9'-0, top of storage 8'-0. To get the 18" clearance, need to be 6" above the bottom flange centered in the 4'-6 dimension. There will be a line of sprinklers in each 4'-6 I-beam pocket. Do I need to be concern with the 4" wide bottom flange if spaced on both sides? I can not meet Table 8.6.5.1.2 and meet the 18" clearance. However, 8.6.5.1.2 (2) states sprinklers are permitted on opposite sides of obstructions not exceeding 4' in width provide you do not exceed sprinkler spacing. Since the sprinklers lines would be 4'-6 o.c. I am o.k. there, so can I ignore the 4" bottom flange since I can not spray under it? Thanks, Gregg Fontes _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum