Below was a checklist I got from one AHJ, FWIW.
DOCUMENTATION REQUIRED FOR REVIEW OF FIRE PUMP INSTALLATIONS A set of drawings and pump information should be provided by the installing contractor as specified in NFPA 20. The submitted set should include: a. Size and rating of the pump and suction supply b. Plan & section views of the overall pump installation, pump house or room, and suction source. c. Layout showing the pump, piping, valving, jockey pump, suction supply, and connection to the underground main etc. d. Diagram showing the internal and external wiring of the controller, including a sequence of operation e. For electric pumps, a drawing showing the physical arrangement of power supply feeding it including a one line diagram f. For diesel driven pumps, a layout of the fuel supply including the size and location of tank, fuel piping arrangement, etc. g. If the pump takes suction from a storage tank provide details of the tank heating system and corrosion protection plan. A copy of the bill of equipment and manufacturer product information sheets with make, model, type, and number of each component in the system should be provided. All equipment used must be either UL listed or FM approved. We will retain one set of drawings and the manufacturer's information supplied for our use in field review of the finished system. ----------------------------------------------------------------------------------------------------------- Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SCĀ 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 craig.pr...@ch2m.com -----Original Message----- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks Sent: Thursday, December 20, 2012 4:24 PM To: sprinklerforum@firesprinkler.org Subject: NFPA 20 Shop Drawings Seems as though there are no documentation requirements in NFPA 20 (like NFPA 13, Chapter 22) when it comes to submittals and acceptance test results. Am I missing the obvious? Bill Brooks William N. Brooks, P.E. Brooks Fire Protection Engineering Inc. 372 Wilett Drive Severna Park, MD 21146-1904 _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum