As a starting point, I'd look at the listed strainer requirements of NFPA 15 
(2012) Section 5.9.  Many times, refineries and the like will use process water 
which may come directly from a river or otherwise unprocessed source.  API RP 
2030 recommends strainers on any system with discharge openings less than 3/8" 
- normally with 1/8" perforations.  That looks to be 3 times smaller than the 
smallest orifice as a starting point.  Make sure the strainer has a flush-out 
connection that can be used without system shutdown.  Minimum is 2" per many 
refinery minimums.  Also, it may be advisable to provide parallel strainers for 
continuous operation to facilitate periodic cleaning of the strainer at 
intervals based on water quality and strainer obstruction experience.  I would 
also consult with the sprinkler and/or monitor nozzle manufacturer for their 
maximum allowable particulate sizes, particularly on the internal pipe sizing 
of the oscillation mechanism.  Also, is your maximum anti
 cipated flow velocity in the piping going to affect strainer requirements?  
What is the condition of the piping upstream of the system in question?

Ryan Hinson
Burns & McDonnell
Direct: 952-656-3662

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Rod DiBona
Sent: Friday, January 11, 2013 10:37 AM
To: [email protected]
Subject: Water filtration specifications

We have a sprinkler and oscillating water monitor nozzle system that is going 
to be fed from tanks and pumps. The owner is going to be filling the tanks with 
"process water" used at this industrial mine site and has asked us to provide a 
specification telling him what the largest particulate acceptable would be in 
the water. I have searched and can't find anything that addresses this. Seems 
like whatever the standard for potable water is should be fine but I don't know 
what that is. Anyone know off the top of your head? Thanks.

[Description: LOGO_10]
Rod DiBona
Vice President
Rapid Fire Protection
office : (605)348-2342
fax : (605)348-0108
cell : (605)391-3553
www.rapidfireinc.com<http://www.rapidfireinc.com>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130111/76f252c3/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 6561 bytes
Desc: image001.jpg
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130111/76f252c3/attachment.jpg>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to