Art, Ryan, Matt

Thanks for your responses. The owner is installing and maintaining the water 
storage tanks and their supply including the strainers used for filtration. 
They have asked us to provide requirements of our system. As far as the 
sprinkler system goes I think the strainer spec that Ryan mentioned works as 
there are no additional requirements mentioned in any tech sheets for standard 
orifice heads. We have asked the manufacturer of the monitor nozzles to weigh 
in and we will see if they have any data. Absent of that I think the 1/8" 
perforations mentioned in 15 - 5.9 for strainers is as detailed as we need to 
get except that we will provide them with our flows so they can check it 
against their strainer specs. Appreciate the help.

Rod at Rapid

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Art Tiroly
Sent: Friday, January 11, 2013 11:01 AM
To: [email protected]
Subject: RE: Water filtration specifications

Vertical turbine pumps take suction from open ponds and lakes with 1/2" mesh 
screen.

Silt and other vegetation is common. Pendent heads on return bends are 
required. Inspections and flushing will be required.

Particulates will settle to the bottom of the tanks. How to remove excess.

I don't know how to establish particulate size.

More important may be how much mud is coming in.


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Rod DiBona
Sent: Friday, January 11, 2013 11:49 AM
To: [email protected]
Subject: RE: Water filtration specifications

Understand... I think I am going to research the standard for potable water and 
give him that. Thanks.

Rod at Rapid

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matthew J.
Willis
Sent: Friday, January 11, 2013 9:46 AM
To: [email protected]
Subject: RE: Water filtration specifications

Guess I was thinking since the owner asked the question, it may not be microns. 
Also I was considering the fact that potable and process water flows a lot more 
than ours..


R/
Matt

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Rod DiBona
Sent: Friday, January 11, 2013 11:42 AM
To: [email protected]
Subject: RE: Water filtration specifications

My thinking is that we are talking in microns so any water used is going to 
have particulates at some level?

Rod at Rapid

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matthew J.
Willis
Sent: Friday, January 11, 2013 9:39 AM
To: [email protected]
Subject: RE: Water filtration specifications

What happens when those "smallest" particles settle together, then travel 
"En-Masse"


R/
Matt

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Rod DiBona
Sent: Friday, January 11, 2013 11:37 AM
To: [email protected]
Subject: Water filtration specifications

We have a sprinkler and oscillating water monitor nozzle system that is going 
to be fed from tanks and pumps. The owner is going to be filling the tanks with 
"process water" used at this industrial mine site and has asked us to provide a 
specification telling him what the largest particulate acceptable would be in 
the water. I have searched and can't find anything that addresses this. Seems 
like whatever the standard for potable water is should be fine but I don't know 
what that is. Anyone know off the top of your head? Thanks.

[Description: LOGO_10]
Rod DiBona
Vice President
Rapid Fire Protection
office : (605)348-2342
fax : (605)348-0108
cell : (605)391-3553
www.rapidfireinc.com<http://www.rapidfireinc.com>

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20130111/76f252c3/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 6561 bytes
Desc: image001.jpg
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20130111/76f252c3/attachment.jpg>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum



-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2221 / Virus Database: 2637/5525 - Release Date: 01/11/13

_______________________________________________