Dewayne & Greg - Thank you.

That makes more sense, I was misreading 8.15.1.2.8. My ceiling is directly
attached, if they fill the space full of non-combustible insulation
(thankfully my GC is willing) it will not have to be sprinklered and the
3000ft² RA will not apply - and no firestopping into 160ft³ would be
required. 

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax 
(731) 267-4853 cell
www.keyfireprotection.com
 
-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Dewayne
Martinez
Sent: Tuesday, January 29, 2013 6:54 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Concealed Space - composite wood joists

8.15.1.2.6  would normally not require and additional fire stopping on our
part for typical construction.  For a typical 12in TJI spaced 16in O.C. the
required run would have to be over 120ft long before the 160ft^3 is
exceeded.
  
 8.15.1.2.8 is only requiring the insulation in the space BETWEEN the bottom
of joist and the ceiling, not the entire space.  Happens a lot with ACT
ceiling installed 6in below the joists. 

Your right on about 8.15.1.2.7 and the non-3000ft^2 area, unfortunately the
GC's are never wanting to do  this at their cost.

Dewayne

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bobby Gillett
Sent: Monday, January 28, 2013 2:05 PM
To: sprinklerforum@firesprinkler.org
Subject: Concealed Space - compsite wood joists

 

NFPA 13 - 2010:

8.15.1.2.6* <http://codesonline.nfpa.org/a/c.ref/ID00001327787/sec>
Concealed spaces formed by ceilings attached to composite wood joist
construction either directly or onto metal channels not exceeding 1 in.
(25.4 mm) in depth, provided the joist channels are firestopped into volumes
each not exceeding 160 ft3 (4.53 m3) using materials equivalent to the web
construction and at least 3 1/2 in. (90 mm) of batt insulation is installed
at the bottom of the joist channels when the ceiling is attached utilizing
metal channels, shall not require sprinkler protection.

8.15.1.2.7   Concealed spaces entirely filled with noncombustible insulation
shall not require sprinkler protection.

8.15.1.2.8   Concealed spaces within wood joist construction and composite
wood joist construction having noncombustible insulation filling the space
from the ceiling up to the bottom edge of the joist of the roof or floor
deck, provided that in composite wood joist construction the joist channels
are firestopped into volumes each not exceeding 160 ft3 (4.53 m3) to the
full depth of the joist with material equivalent to the web construction,
shall not require sprinkler protection.

 

I have a concealed space formed by composite wood joists with ceiling
attached directly to the bottom of the joist (no metal channels, so
insulation is not a requirement). If I'm not mistaken, in order to consider
it a space that doesn't require sprinkler protection I have to do the
following:

Per 8.15.1.2.6 - Have the joist channels firestopped into volumes not
exceeding 160 ft³ OR

Per 8.15.1.2.7 - Completely fill the space with noncombustible insulation OR

Per 8.15.1.2.8 - Completely fill the space with noncombustible insulation
AND have the joist channels firestopped into volumes not exceeding 160 ft³
(WHICH KICKS 8.15.1.2.7 OUT FOR COMPOSITE WOOD JOISTS ALTOGETHER)

 

I guess what I am misunderstanding is if I have to firestop the joist
channels into volumes not exceeding 160ft³ either way, why would we want to
fill the joist space completely with noncombustible insulation? Only thing I
could think of would be to keep from having to do a 3000ft² RA in the
adjacent protected space. 

 

Any comments for my understanding would be appreciated.

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <http://www.keyfireprotection.com> www.keyfireprotection.com

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20130128/9cef5418/attachment.html>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2013.0.2890 / Virus Database: 2639/6064 - Release Date: 01/28/13

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to