This from a Fire Marshal for a large University in AZ. We were having trouble 
locating hose valves in the one story area of the building. There are only two 
stairs in the building and they are more than 200 ft. from parts of the 
gymnasium. We reviewed the code and offered a credit to delete the standpipe 
system because we didn't think it was required. This the response from the FM. 
He wants all interior points to be with 150 feet from where they park a fire 
truck.

"If you send a too scale plan from where fire trucks will be at all points of 
entry to the building and can show that nothing is more than 150' I will 
entertain the suggestion of no standpipes.  I have seen everything that ****** 
has been shown and it is not represented well.  This includes the existing 
building since the existing building had adequate coverage and did not need a 
standpipe before the add-on.  Now that there is an add-on where there is no 
access at the center point it affects both the new and old and we need 
assurance with a too scale drawing from fire truck to all areas of all floors.  
Discussing it does not solve anything until you can also prove it on paper too 
scale "as the hose lays and not the crow flys."

I have difficulty finding a way to talk to someone like this. 

Ron Fletcher
Aero Phoenix