Interesting interpretation.

FYI, the 2012 edition removed "and in the locations indicated in Section905.4, 
905.5, and 905.6".

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Fairchild, Jack [mailto:[email protected]] 
Sent: Tuesday, January 29, 2013 12:44 PM
To: [email protected]
Subject: RE: Fire Marshal requirement?

2009 IFC 905.3 read strictly does not tie standpipe hose connections to height. 
 It states ..."where required by sections 905.3.1 through 905.3.7 and in the 
locations indicated in Sections 905.4, 905.5, and 905.6."  Section 905.4 needs 
to be applied regardless of 905.3.1 because of the "and" after 905.3.1 in 
section 905.3.  (wow that's wordy).

Personally I do not believe the intent is to provide hose connections in any 
building that has more than one floor or where the fire truck is more than 200 
feet from any point in the building, but I see how it could be read that way.  
I always thought 905.4 was intended for very expansive buildings such as those 
seen out west.  Maybe this section should be tied to a square footage.

Jack Fairchild


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Johnson, Duane 
(NIH/OD/ORS) [C]
Sent: Tuesday, January 29, 2013 12:21 PM
To: '[email protected]'
Subject: RE: Fire Marshal requirement?

Per IBC:

905.3.1  Class III standpipe systems shall be installed throughout buildings 
where the floor level of the highest story is located more than 30 feet (9144 
mm) above the lowest level of fire department vehicle access, or where the 
floor level of the lowest story is located more than 30 feet (9144 mm) below 
the highest level of fire department vehicle access.

STORY. That portion of a building included between the upper surface of a floor 
and the upper surface of the floor or roof next above (also see "Basement," 
"Building height," "Grade plane" and "Mezzanine"). It is measured as the 
vertical distance from top to top of two successive tiers of beams or finished 
floor surfaces and, for the topmost story, from the top of the floor finish to 
the top of the ceiling joists or, where there is not a ceiling, to the top of 
the roof rafters.

MEZZANINE. An intermediate level or levels between the floor and ceiling of any 
story and in accordance with Section 505.

505.2 Mezzanines.
A mezzanine or mezzanines in compliance with Section 505.2 shall be considered 
a portion of the story below.

A 32' high mezzanine doesn't constitute standpipes.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor) Office of Research Services National 
Institutes of Health
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: [email protected] [mailto:[email protected]]
Sent: Tuesday, January 29, 2013 11:59 AM
To: [email protected]
Subject: RE: Fire Marshal requirement?

A small 2 story area the rest is all one story. There is a running track on a 
mezzanine that circles the gym that is at 32 ft. high but it is open to the 
gym. This is an addition to a building that is sprinklered but without 
standpipes. The new addition meets all the exiting and egress requirements so 
that is not an issue.

Ron Fletcher
Aero Phoenix

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Tuesday, January 29, 2013 9:36 AM
To: [email protected]
Subject: RE: Fire Marshal requirement?

How many stories is the building, and on what floor is this condition?


Steve Leyton



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, January 29, 2013 7:16 AM
To: [email protected]
Subject: Fire Marshal requirement?

This from a Fire Marshal for a large University in AZ. We were having trouble 
locating hose valves in the one story area of the building.
There are only two stairs in the building and they are more than 200 ft.
from parts of the gymnasium. We reviewed the code and offered a credit to 
delete the standpipe system because we didn't think it was required.
This the response from the FM. He wants all interior points to be with
150 feet from where they park a fire truck.

"If you send a too scale plan from where fire trucks will be at all points of 
entry to the building and can show that nothing is more than 150' I will 
entertain the suggestion of no standpipes.  I have seen everything that ****** 
has been shown and it is not represented well.
This includes the existing building since the existing building had adequate 
coverage and did not need a standpipe before the add-on.  Now that there is an 
add-on where there is no access at the center point it affects both the new and 
old and we need assurance with a too scale drawing from fire truck to all areas 
of all floors.  Discussing it does not solve anything until you can also prove 
it on paper too scale "as the hose lays and not the crow flys."

I have difficulty finding a way to talk to someone like this. 

Ron Fletcher
Aero Phoenix

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to