I know of one reviewer in the area that would say "what if" a fire
started at the intersection of the two types of heads and make us put a
remote area there.  
Thanks for the info Ron.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Thursday, January 31, 2013 11:14 AM
To: [email protected]
Subject: RE: Mixing ESFR sprinklers due to building height

Yes, we have come across it many times. Some buildings have ridge
heights over 40' and eave heights under 40'. There is no good way, that
we have found, to mix k17's and k25's in the same system. The higher
pressure required by the k17's causes the K25's to over flow. We always
change at system breaks to k17's once the roof height is less than 40'.
I don't see the need to be concerned about going 15 ft beyond.

Ron Fletcher
Aero Phoenix 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Thursday, January 31, 2013 10:08 AM
To: SprinklerFORUM
Subject: Mixing ESFR sprinklers due to building height

This one came across for bidding and the specs / design are from the
consultant's drawings.  The overall building height requires the use of
K25 ESFR sprinklers.  The consultant has specified that K25 ESFR
sprinklers are to be used only in the high bay of the building at
pressure "A" and K17 ESFR sprinklers at pressure "B" are to be used for
the lower areas.  The building is open joists / girders type of
construction.  Can this even be done?  If so, I imagine that 3 calcs
would be in order.  A K25 calc, K17 calc, and the area where they would
overlap (ie 15ft beyond).

Anyone else come across something like this?

Thanks,

 

Dewayne Martinez

Design Build Fire Protection

262-784-7900 (w)

262-784-8401 (f)

414-349-0468 (cell)

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20130131/7b637fe5/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to