I would see it as not being that relevant in regards to the installation being 
in a warehouse or a mall.  NFPA 13-2013 does not address different criteria for 
different occupancies. 


Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Sharon Alves
Sent: Thursday, March 14, 2013 11:34 AM
To: [email protected]
Subject: RE: HVLS Fans

Thank you for all of your replies.  With these studies, the testing was 
performed in a warehouse with storage. In these scenarios, the  performance is 
quite specific. With my project, an open 40' high mall concept, the AHJ is 
asking what affect the fans will have on the performance not only of the fire 
sprinkler activation, but the heat and smoke detectors as well.  


Thank you,

SHARON ALVES
Senior Fire Sprinkler Designer

LP Consulting Engineers, Inc.
Mechanical -MElectrical -EPlumbing Engineers - Fire Protection
1663 Eureka Road
Roseville, CA 95661
P: 916.771.0778 - F: 916.783.9446
[email protected]
www.lpengineers.com

This email and its attachments are the sole property of LP Consulting 
Engineers, Inc. and Copyrighted by LP Consulting Engineers, Inc. 2013.  This 
communication with its contents may contain confidential and/or legally 
privileged information. It is solely for the use of the intended recipient(s). 
Unauthorized interception, review, use or disclosure is prohibited and may 
violate applicable laws including the Electronic Communications Privacy Act. If 
you are not the intended recipient, please contact the sender and destroy all 
copies of the communication.  The sender and its company do not guarantee that 
this email or its attachments is free of viruses nor does it accept any 
liability for same.



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Matthew J. Willis
Sent: Thursday, March 14, 2013 4:35 AM
To: [email protected]
Subject: RE: HVLS Fans

I am dealing with this right now on a car dealership (service area). The 
research conducted won an award in 2012. It is all still new and making its way 
into the codes now. Bottom line, sprinklers will work and not be obstructed, 
but the fan needs to be shut down within 90 seconds. Some have this built in 
others may not. The only thing I could think of if not is a shunt trip like we 
use in elevators.
Here is a video from a leading expert that helps...



http://www.youtube.com/watch?v=gEjjr_v2vis


R/
Matt

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of AKS-Gmail-IMAP
Sent: Thursday, March 14, 2013 12:19 AM
To: [email protected]
Subject: Re: HVLS Fans

No, but it makes sense to turn them off upon smoke detection so that they allow 
the smoke to collect and stay up near the roof away from the public.
An air sampling smoke detection manufacturer claims their detector is built 
into BA fans for this purpose, but that seems like a bad idea for maintenance 
reasons. If it is a basketball gym then make sure the fans are structuraly 
decoupled from the basketball goals. That might be very hard to do. Gym roof 
are light. Otherwise you'll be getting a call from the owner about the hoops 
vibrating with the fans.  

Allan Seidel
St. Louis, MO

On Mar 13, 2013, at 6:23 PM, Sharon Alves <[email protected]> wrote:

> Has anyone had any experience with the HVLS fans in facilities other 
> than storage?
> 
> 
> 
> Thank you,
> 
> 
> 
> SHARON ALVES
> 
> Senior Fire Sprinkler Designer
> 
> 
> 
> LP Consulting Engineers, Inc.
> 
> Mechanical - Electrical - Plumbing Engineers - Fire Protection
> 
> 1663 Eureka Road
> 
> Roseville, CA 95661
> 
> P: 916.771.0778 - F: 916.783.9446
> 
> <mailto:[email protected]> [email protected]
> 
> www.lpengineers.com
> 
> 
> 
> This email and its attachments are the sole property of LP Consulting 
> Engineers, Inc. and Copyrighted by LP Consulting Engineers, Inc. 2013.
> This communication with its contents may contain confidential and/or 
> legally privileged information. It is solely for the use of the 
> intended recipient(s). Unauthorized interception, review, use or 
> disclosure is prohibited and may violate applicable laws including the 
> Electronic Communications Privacy Act. If you are not the intended 
> recipient, please contact the sender and destroy all copies of the 
> communication.  The sender and its company do not guarantee that this 
> email or its attachments is free of viruses nor does it accept any
liability for same.
> 
> 
> 
> -------------- next part -------------- An HTML attachment was 
> scrubbed...
> URL: 
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta
> chments/20130313/11dbf91f/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to