Thank you all for your comments and help.  The meeting went well today and
was actually a presentation as to how the information was derived.  Very
good and helpful.  The short of the long is, so long as you have a geo tech
report on the soils and the numbers work out to place you in the right
category A or B, seismic rules do not apply.

Again, I want to thank everyone for your input it helped me to be informed
going into today's meeting.

Thanks, 

Bob Knight, CET III
208-318-3057
www.firebyknight.com



-----Original Message-----
From: ParsleyConsulting [mailto:parsleyconsult...@cox.net] 
Sent: Friday, March 15, 2013 9:24 AM
To: b...@firebyknight.com; sprinklerforum@firesprinkler.org
Subject: Re: Seismic and ASCE 7

Bob, and everyone else who weighed in on this,

     My apologies for not chiming in sooner, I was away from the office
yesterday.

     ASCE7 is the basis for "when" fire sprinkler systems require seismic
protection, and while I'm not sure about other states, here in California
that document is adopted by reference in the California Building Code.  You
may want to check the building code in your area to see if it doesn't
include ASCE7 as an "adopted" or "referenced" 
standard.  You'll also find it in the referenced publications (section 2.3),
of the 2010 edition of NFPA 13, which indicates to my non-lawyer eyes that
it is "considered part of the requirements" of NFPA 13.

     Both ASCE7 (in section 11), and the IBC (in section 1613) provide a
means to establish the seismic design category.  It's also worth noting that
IBC references ASCE7 in the process. The only variable which is complicated
in the process of establishing the SDC is the "Site Class", as it involves
some soil considerations which truly should be made by an engineer of
record.  The default class is presumed to be "D", however this should not be
a decision made by a fire sprinkler contractor.

     Once the SDC has been established, there is little left to review,
because the remaining calculations are simple math and values from tables.
ASCE7-10, notes in section 13.1.4 (4) that "mechanical and electrical
components in seismic design category B" are exempt from requiring seismic
protection.  The very next "exemption" states that "mechanical and
electrical components in seismic design category C [are exempt] provided
that the component importance factor (Ip) is equal to 1.0".  Section 13.1.3
specifies that "...the component importance factor shall be 1.5 if....(1)
the component is required to function for life-safety purposes after an
earthquake, including fire sprinkler systems...."

     And, eventually, ASCE7 section 13.6.8.2, gets around to advising that
"Fire protection sprinkler piping, pipe hangers, and bracing designed and
constructed in accordance with NFPA 13 shall be deemed to meet the force and
displacement requirements of this section."  That is also the conclusion
reached by the IBC in section 1613.6.3.

     So, Bob, to your question, if the building is indeed in design category
"B", no seismic protection is required for the fire sprinkler system by
ASCE7 or the IBC.  Any category higher than that (C-D-E-F), will require
seismic protection.

     Hope that helps.

PARSLEY CONSULTING

Ken Wagoner, SET

760.745.6181 voice

760.745.0537 fax

parsleyconsult...@cox.net <mailto:parsleyconsult...@cox.net>e-mail

www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website

IMPORTANT NOTICE: This correspondence is not a Formal Interpretation issued
pursuant to NFPA Regulations. Any opinion expressed is the personal opinion
of the author and does not necessarily represent the official position of
the NFPA or its Technical Committees. In addition, this correspondence is
neither intended, nor should it be relied upon, to provide professional
consultation or services.


On 3/14/2013 3:03 PM, Bob wrote:
> There is a project that I am not involved in, but the AHJ called for 
> an opinion.  The situation revolves around the idea that if a building 
> is in site class C and design category B, the sway bracing 
> requirements of NFPA 13 are waved by ASCE 7.  I have not come across 
> this before, and there is a certain fire sprinkler contractor that is 
> eliminating the sway bracing, retaining straps, etc... on several 
> large warehouse / distribution buildings.  The claim is that ASCE 7 
> allows for this.  Has anyone come across this and have information 
> verifying or negating it?  I am meeting with several AHJ's in regard 
> to this tomorrow morning, so any input will be extremely useful.
>
> Thank you,
>
> Bob Knight, CET III
> 208-318-3057
> www.firebyknight.com

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to