I don't have the data sheets in front of me, but don't you need 2535 sq ft? 1500 +30%+30% unless you are doing the fixed number of heads.
Travis Mack, SET MFP Design, LLC Sent from my iPhone On Mar 20, 2013, at 7:38 PM, Greg McGahan <[email protected]> wrote: > I am not following you on the Hip - AP PLUS BB's to get to 1,950 sqft? I > get the other one..... > > On Wed, Mar 20, 2013 at 9:29 PM, Bob <[email protected]> wrote: > >> Greg, >> If I understand, you will have two calcs. One at the hip that includes AP >> & >> BB sprinklers up to your 1950 sf, than you will have a calc following >> Figure >> 20-B-2. This is similar to what Figure 22 shows which references 20-C-3. >> The only difference with your scenario is where the two AP sprinklers are >> picked up, but this should still fulfill the intent. >> >> >> Bob Knight, CET III >> 208-318-3057 >> www.firebyknight.com >> >> >> >> -----Original Message----- >> From: [email protected] >> [mailto:[email protected]] On Behalf Of Greg >> McGahan >> Sent: Wednesday, March 20, 2013 8:06 PM >> To: [email protected] >> Subject: Tyco BB and AP sprinklers >> >> OK, working late and can't figure this on out conclusively....not diagrams >> match this case. >> >> If you use BB heads at the peak of an attic with AP sprinklers at the hip >> on >> each end of the building and on elone at the eave along the entire length >> of >> the building since the bldg is over 60'-0" wide. >> Figure 22 identifies the Dry System with BB's and the AP's at the peak, but >> doesn't show the eave AP's. >> Figure 20-B-2 identifies the BB heads and AP heads at the eave, but doesn't >> show the hip. >> >> I assume you have to follow the guidelines of Figure 22 and calculate 1,950 >> sqft including the hip and eaves until I get the 1,950 sqft.....anybody >> know? >> >> Thanks, >> >> >> -- >> Greg McGahan >> Living Water Fire Protection, LLC <http://www.livingwaterfp.com> >> 1160 McKenzie Road >> Cantonment, FL 32533 >> 850-937-1850 >> fax 850-937-1852 >> -------------- next part -------------- >> An HTML attachment was scrubbed... >> URL: >> < >> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment >> s/20130320/33bb69fe/attachment.html> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum >> ----- >> No virus found in this message. >> Checked by AVG - www.avg.com >> Version: 2013.0.2904 / Virus Database: 2641/6191 - Release Date: 03/20/13 >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > -- > Greg McGahan > Living Water Fire Protection, LLC <http://www.livingwaterfp.com> > 1160 McKenzie Road > Cantonment, FL 32533 > 850-937-1850 > fax 850-937-1852 > -------------- next part -------------- > An HTML attachment was scrubbed... > URL: > <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130320/698d587e/attachment.html> > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum