FM do very much care about pallets - so much so there is a data sheet 
especially for idle pallets 8-24.
We found out that fire tests for 8-9 for plastic commodities were done using 
plastic pallets, so we challenged them as to why we couldn't use the criteria 
from 8-9 to protect idle pallets (rather than the outdated requirements of 
8-24).
They accepted this and we used this approach on several projects.
Just rewritten, data sheet 8-24 now refers to plastic pallets as an uncartoned 
unexpanded plastic - to be protected in accordance with 8-9!

8-1 also refers to plastic pallets supporting commodities and increasing 
classification, but doesn't refer to flammable liquids.

In 8-1, once you get to plastic commodities the plastic pallet has no effect on 
the classification.  I expect it is the same with flammable liquids at a 
certain point.
It would be worth asking the FM Global engineer on the project - the data 
sheets have unpublished information for FM only that may shed some more light 
on it.

Not a full answer to your question, but hope it helps.

Nicky Marshall
Branch Manager (Blenheim)

Protech Design
Specialist Fire Protection Consultants
03 579 5577
021 433 488
www.protechdesign.co.nz 
skype: nicky-marshall
105A Alabama Rd, Redwoodtown, Blenheim 7201, New Zealand
PO Box 4022, Redwood Village, Blenheim 7242, New Zealand


-----Original Message-----
From: Ben Young [mailto:[email protected]] 
Sent: Tuesday, 9 April 2013 1:03 a.m.
To: [email protected]
Subject: Plastic Pallets for FM design

Fellow forumites,

I'm doing a flammable liquids storage area design under FM 7-29, and I cannot 
find any specific information on the need (or not) to increase the design 
requirements if plastic pallets are used.

I'm storing an ignitable liquid with a flash point <200°F in 55 gallon 
relieving-style metal drums on-end in a palletized configuration.  I'm using 
Table 7 from 7-29 for this.

I did a search for plastic pallets in both 7-29 and 2-0 but found no references 
to having to increase the design for this. 7-29 does list some increases for 
the use of plastic pallets, but these only pertain atypical ignitable liquids, 
which mine does not fall under.

I didn't find anything from searching 2-0 either.  Did I skip something basic 
here, or does FM not really care about plastic pallets?

Thanks for any assistance.

Benjamin Young
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130408/e31351e9/attachment.html>


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to