2011 NEC, then again you probably knew this.

695.3 Power Source(s) for Electric Motor-Driven Fire
Pumps. Electric motor-driven fire pumps shall have a reliable
source of power.

(A) Individual Sources. Where reliable, and where capable
of carrying indefinitely the sum of the locked-rotor current of
the fire pump motor(s) and the pressure maintenance pump
motor(s) and the full-load current of the associated fire pump
accessory equipment when connected to this power supply,
the power source for an electric motor driven fire pump shall
be one or more of the following.

(1) Electric Utility Service Connection. A fire pump shall
be permitted to be supplied by a separate service, or from a
connection located ahead of and not within the same cabinet,
enclosure, or vertical switchboard section as the service
disconnecting means. The connection shall be located and
arranged so as to minimize the possibility of damage by fire
from within the premises and from exposing hazards. A tap
ahead of the service disconnecting means shall comply with
230.82(5). The service equipment shall comply with the
labeling requirements in 230.2 and the location requirements
in 230.72(B). [20:9.2.2(1)]

(2) On-Site Power Production Facility. A fire pump shall
be permitted to be supplied by an on-site power production
facility. The source facility shall be located and protected to
minimize the possibility of damage by fire. [20:9.2.2(3)]

(3) Dedicated Feeder. A dedicated feeder shall be permitted
where it is derived from a service connection as described
in 695.3(A)(1). [20:9.2.2(3)]

(B) Multiple Sources. If reliable power cannot be obtained
from a source described in 695.3(A), power shall be
supplied by one of the following: [20:9.3.2]

(1) Individual Sources. An approved combination of two
or more of the sources from 695.3(A).

(2) Individual Source and On-site Standby Generator.
An approved combination of one or more of the sources in
695.3(A) and an on-site standby generator complying with
695.3(D). [20:9.3.4]

Exception to (B)(1) and (B)(2): An alternate source of
power shall not be required where a back-up engine-driven
or back-up steam turbine-driven fire pump is installed [20:9.3.3]

Also phase converters are out

(F) Phase Converters. Phase converters shall not be permitted
to be used for fire pump service. [20:9.1.7]

Sounds like a Diesel, use the  single phase service for the controller,
heater, jockey, etc.


John Drucker, CET
Fire Protection Subcode Official
Fire / Building / Electrical Inspector
New Jersey



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Monday, April 8, 2013 9:25 PM
To: [email protected]
Subject: Re: generator as primary supply

Only if you really stretch the definition

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080
www.fpdc.com


On Apr 8, 2013, at 9:13 PM, "John Drucker" <[email protected]> wrote:

> Does it qualify as a power production facility John Drucker - Mobile 
> Email
> 
> ----- Original Message -----
> From: [email protected] 
> <[email protected]>
> To: [email protected] 
> <[email protected]>
> Sent: Mon Apr 08 20:40:33 2013
> Subject: generator as primary supply
> 
> I am looking at a job where the spec calls for an electric VT fire pump
with a generator as primary electric supply. (Only single phase in street.)
I know it can be done mechanically but I am not aware of any approved
system. Is there such an animal?
> 
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> 
> CONFIDENTIAL AND PROPRIETARY:
> This email message is intended only for the use of the individual or
entity to which it is addressed and may contain information that is
privileged and confidential, nor is it, unless specifically stated, intended
to be relied upon by any person or persons other than the individual or
entity named above and no warranties or representations are made or intended
to persons or entities not named above.  If the reader is not the intended
recipient, you are hereby notified that any dissemination, distribution or
copying of this communication is strictly prohibited.  If you have received
this communication in error, please notify us immediately by telephone,
return this message to the address above and delete all copies.  Thank you.
> 
> -------------- next part -------------- An HTML attachment was 
> scrubbed...
> URL: 
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta
> chments/20130408/37aeeda5/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to