I agree that the diesel is the way to go, but wanted to be sure I wasn't 
missing something before I shoot my mouth off (for once). Lots of problems with 
this project. The Engineer has little knowledge of sprinkler systems or Codes.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com

On Apr 9, 2013, at 11:05 AM, <[email protected]> wrote:

> I'd second that recommendation.  Going electric with a generator makes no 
> sense.  Go Diesel and be done with it.  I did a project in 2011 with 4000 gpm 
> diesel driven VT's.  
> 
> Plus, nowhere in NFPA 20 does it state that a generator is permitted as the 
> primary power source.  Every text you find related to a generator is stating 
> use as an alternate or backup power source.
> 
> Craig L. Prahl, CET   
> Fire Protection 
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
> 
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Art Tiroly
> Sent: Tuesday, April 09, 2013 10:46 AM
> To: [email protected]
> Subject: RE: generator as primary supply
> 
> May I suggest that you consider a diesel driver with a right angle gear drive 
> for the VT pump. This is an approved method and likely less costly.
> 
> 
> Arthur Tiroly
> ATCO Fire Protection Design
> Tiroly and Associates
> 24400 Highland Rd rm 25, CLE 44143
> 216-621-8899
> 216-570-7030 Cell