My intention is to connect a 1-1/2" T to the domestic line and put a riser, 
complete with backflow, for each system. That would be required with an FDC. I 
would go along with the three 13D systems, but I don't think the AHJ is going 
to buy into that. Besides, this will more than likely end up in front of the MA 
Sprinkler Review Board and I don't want to (and am not getting paid to) get 
into that fight.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com

On Apr 18, 2013, at 10:23 AM, "Steve Leyton" <[email protected]> wrote:

> Ummm ... I don't think that's the intent of a 13R design.  Sounds more
> like three 13D or IRC systems in a row.    And I think you have a
> plumbing code issue: you can't have an FDC that's backfed to each of
> three systems that are in turn connected to domestic water unless you
> limit your inlet pressure to 80psi and/or put a BFP on each of the
> sprinkler connections.   Dude, just say no to this set up.
> 
> The foregoing is my opinion only and does not necessarily represent the
> opinion or intent of the NFPA 13D/13R Technical Committee on Residential
> Sprinkler Systems.
> 
> Steve Leyton
> Protection Design & Consulting
> San Diego, CA
> 
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> Todd - Work
> Sent: Thursday, April 18, 2013 7:14 AM
> To: [email protected]
> Subject: 13R FDC with multiple risers
> 
> I am designed a 13R system to be retrofitted into a 3 family house (all
> 3 units are 1st floor only). Each unit has an 1-1/2" feed for domestic
> water, to which the sprinkler risers will be connected. I will end up
> with 3 risers, one for each unit. Any thoughts on how to handle the FDC?
> A pit on the line with a check and free standing FDC is impractical.
> Individual FDCs seem like overkill. There is no real way to interconnect
> the systems due to building configuration. 
> 
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to