Tim,

First I am working under the IFC 2012 that requires sprinkler systems to be 
electronically monitored with supervising central station.

Per Section NFPA 72, 2010 10.15  and the definitions of a Fire Alarm Control 
Unit and Dedicated Function Fire Alarm Control Unit, a smoke detector is 
required to be located above the fire pump control panel.

Daniel S. Failla Jr.
Assistant Fire Marshal
Charleston Fire Marshal's Office
75 Calhoun Street
3rd Floor
Charleston, SC 29401
Office - 843 - 724 - 5960
Email: [email protected]

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Easter, 
Timothy
Sent: Tuesday, May 07, 2013 11:35 AM
To: [email protected]
Subject: fire pump controller detection requirement

I know smoke detectors are required within 5' of FACP/MNS panels, what about 
fire pump controller panels?

Regards,

Timothy Easter
E.I.T.
Graduate Fire Protection Engineer
URS Corporation