I agree a pump controller is not a FACU and thus does not require a smoke 
detector. 
An FACU requires:
Secondary power...which they don't have, secondary source of power might be 
connected but in itself doesn't.   
Input from initiating devices...Can't say I've ever seen an initiating device 
connected.  It actually is an initiating device, kinda.   
Processes these signals...Not a lot of processing going on.  
To determine required fire alarm system output...best I know they don't create 
FA output functions like turn on the horns and strobes. The real FACU decides 
what to do with the FPC outputs, mostly supervisory signals.

3.3.92*Fire Alarm Control Unit.(FACU) A component of the fire alarm system, 
provided with primary and secondary power sources, which receives signals from 
initiating devices or other fire alarm control units, and processes these 
signals to determine part or all of the required fire alarm system output 
function(s). (SIG-PRO)

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bill Brooks
Sent: Tuesday, May 07, 2013 2:38 PM
To: [email protected]
Subject: RE: fire pump controller detection requirement

So, if it does not have a secondary power source it would not be a Dedicated 
Function Fire Alarm Control Unit?

I don't believe the committee had a fire pump controller in mind when this 
change was made. I never have thought of a fire pump controller as a component 
of a fire alarm system, but I'm willing to be educated.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Failla, 
Daniel
Sent: Tuesday, May 07, 2013 2:52 PM
To: '[email protected]'
Subject: RE: fire pump controller detection requirement

Tim,

First I am working under the IFC 2012 that requires sprinkler systems to be 
electronically monitored with supervising central station.

Per Section NFPA 72, 2010 10.15  and the definitions of a Fire Alarm Control 
Unit and Dedicated Function Fire Alarm Control Unit, a smoke detector is 
required to be located above the fire pump control panel.

Daniel S. Failla Jr.
Assistant Fire Marshal
Charleston Fire Marshal's Office
75 Calhoun Street
3rd Floor
Charleston, SC 29401
Office - 843 - 724 - 5960
Email: [email protected]

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Easter, 
Timothy
Sent: Tuesday, May 07, 2013 11:35 AM
To: [email protected]
Subject: fire pump controller detection requirement

I know smoke detectors are required within 5' of FACP/MNS panels, what about 
fire pump controller panels?

Regards,

Timothy Easter
E.I.T.
Graduate Fire Protection Engineer
URS Corporation
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to