In concrete tee construction placing the sprinkler def 1" below the bottom of 
tee is one option.  When you've got clearance problems you may have to pocket 
the lines between the tees.  Makes it more expensive but sometimes you have no 
other option.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jay White
Sent: Wednesday, May 08, 2013 9:04 AM
To: [email protected]
Subject: Sprinkler Design Of Parking Garage

The IBC Code says you have to have 7'0" clearance in a parking garage. We are 
having elevation clearance problems with our sprinkler pipe. Does anyone know 
of a exception to the code that allows you to be below 7'-0"? Concrete tee 
construction. Bottom of the tee is 7'-3 ¼".  Deflector has to maintain a 1" 
mninimum from bottom of tee. Dry system installed. Any help would be 
appreciated.

 