We have gotten exceptions for 6'-8" before...(door height)
On May 8, 2013 9:03 AM, "Jay White" <[email protected]> wrote:

> The IBC Code says you have to have 7’0” clearance in a parking garage. We
> are having elevation clearance problems with our sprinkler pipe. Does
> anyone
> know of a exception to the code that allows you to be below 7’-0”? Concrete
> tee construction. Bottom of the tee is 7’-3 ¼”.  Deflector has to maintain
> a
> 1” mninimum from bottom of tee. Dry system installed. Any help would be
> appreciated.
>
>
>
> Jay White
>