Thanks John. This is not a physical change, and it should be called
Adjusting the Pressure. A denser fluid flows slower, so if we used K=5.6 and
P=7 PSI for the 65.5 lb/ft3 fluid, it would take 61.5 seconds to put 14.82
gallons on the floor, instead of 60 sec.. The higher the Pn, the faster it
flows. By "saying" the K is smaller than it actually is, the appropriate
increase in PSI will be required.
I just hope I have understood what you are saying. Thanks Again.
I will look at 2013 next chance I get.

-----Original Message-----
From: John Denhardt [mailto:[email protected]] 
Sent: Tuesday, June 11, 2013 4:42 PM
To: [email protected]
Subject: RE: adjusting the K-Factor with our bare hands

Keep in mind that you started with a nominal K factor of 5.6.  Per Table
6.2.3.1 (NFPA 13 - 2007), the range for the K factor under laboratory
testing conditions was 5.3 to 5.8.  Just talking out loud, but I wonder if
that correction is really that important when the reality is the base number
could be off by 0.5 to start.

Look at NFPA 13 - 2013 and see if these adjustments are still required.  My
educated guess is that they have been deleted based on this argument.  Check
the ROP and the ROC from last cycle if you are interested.

John - This is my personal opinion and not an official interpretation by the
NFPA 13's technical committee.

John August Denhardt, P.E., FSFPE
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES - Can you live without them?


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Casterline
Sent: Tuesday, June 11, 2013 7:52 AM
To: [email protected]
Subject: adjusting the K-Factor with our bare hands

>From NFPA 13-2007, 22.4.4.5.1, we are required to, among other things,
adjust the K-Factor. 

Using  the Hazen-Williams friction formula, 62.4 lb/ft3 / 144 in2 = .433
lb/in2/ft(h).

If we have an AF solution at 65.5 lb/ft3, / 144 = .455 lb/in2/ft(h).

If K=5.6, and we assume P=7 PSI.:

7/.433=16.166 ft(h). 7/.455=15.385 ft(h).*

15.385/16.166=.952. sqrt(.952)=.976, x 5.6 = 5.46.

There is a chart in 13 showing a 50% glycerin solution at about -10F
weighing about 15% more than 100% water: 62.4 x 1.15 = 71.76.
71.76/144=.498. 7/.498=14.056 ft(h). 14.056/16.166=.869. sqrt(.869)=.932, x
5.6 = 5.22.

If I had to fab the pipe today and formalize the submittal tomorrow (after
googling centipoises for several hours) I would calc it like it was 'all
wet', using K=5.22.  

* converting PSI to feet of head(h) it is seen that the denser the solution,
the 'shorter' it is. Since v=sqrt(2gh), the shorter it is the slower it is.
Making the adjustment based on "h", we have to take the square root of the
ratio, i.e., (K=Q/sqrtP). If adjusted based on velocity we would use the
ratio itself (square feet=cubic feet per second divided by feet per second):
sqrt(2*32.2*16.166)=32.266 ft/sec.

sqrt(2*32.2*15.385)=31.477 ft/sec.

31.477/32.266=.976.

 

The above is simply the type of thing I enjoy doing and like to share,
hoping it will cause no harm, to be taken or left as one sees fit.

 

thanks,

 

Brad Casterline, NICET IV

Fire Protection Division

 

FSC, Inc.

P: 913-722-3473

[email protected]

www.fsc-inc.com

 

Engineering Solutions for the Built Environment

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to