Right. I think the question was answered with the suggested heads (I haven't 
looked at them yet) than can be used at .15 in oh2 with a larger remote area. 

Thanks
Greg

Sent from my iPhone

On Jun 30, 2013, at 10:22 AM, "Cahill, Christopher" <[email protected]> 
wrote:

> Correct, you still calc them but take the flow hit in the main not the flow 
> and pressure hit in the RA bl. Often this looks like feeding the new heads in 
> the RA from a bl connection 3 or 4 lines over. Vice versa if there are a lot 
> of heads to be added.
> 
> Chris Cahill
> Burns & McDonnell
> Fire Protection Engineer
> 952-656-3652
> [email protected] Ron Greenman wrote:
> Chris can tell me if I'm reading too much into what he said, but the
> picture I got from his suggestion was putting in a new branchline to supply
> the new heads. That would be less demanding than adding those heads to
> existing branchlines. If the heads are in the design area then they have to
> be included.
> 
> 
> On Sun, Jun 30, 2013 at 7:46 AM, Greg McGahan <[email protected]> wrote:
> 
>> I don't see any way you can avoid these heads being in the remote area no
>> matter how you feed them.
>> 
>> With the new heads the spacing in the center of the grid will be 10 x 20.
>> 
>> Sent from my iPhone
>> 
>> On Jun 30, 2013, at 9:22 AM, "Cahill, Christopher" <[email protected]>
>> wrote:
>> 
>>> I assmue you are cutting heads into the existing bl's causing you to add
>> another head to the bl on the calcs. You can always run a new bl such that
>> the flow never hits the existing bl in the remote area. More costly? A
>> little but cheaper than replacing the existing system.
>>> 
>>> Chris Cahill
>>> Burns & McDonnell
>>> Fire Protection Engineer
>>> 952-656-3652
>>> [email protected] Greg McGahan wrote:
>>> Hello,
>>> 
>>> We have an existing system installed 20 x 20 with 14.5K ECOH sprinklers.
>> They have now installed  a new wall separating the space into 2 spaces and
>> left the sprinklers overspaced off the wall. The Calc plate indicates that
>> the design was originally .15 fpm over 2,000 soft  and when we re-calc the
>> system we are nearly identical to the results recorded on the data plate.
>> If we calculate it at .20/1,500 it does not work.
>>> 
>>> Question is how to we even begin to sort this out in order to add a row
>> of new heads to correct the overspacing? The new sprinklers all seem to be
>> specifically listed for .20 (OH2) and i do not see a loophole to utilize a
>> lower density and a larger Remote Area as in the original design. I also do
>> not see an allowance in 13 for such a scenario (similar to the allowance
>> for modifications to existing systems with residential heads that were
>> originally designed for less than 7 psi end head pressure)
>>> 
>>> I do not think there will be any salvaging this system if we cannot
>> reduce the density…
>>> 
>>> Thanks for any help,
>>> Greg
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> 
> 
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
> 
> [email protected]
> 
> http://www.bates.ctc.edu/fireprotection/
> 
> 253.680.7346
> 253.576.9700 (cell)
> 
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> 
> They are happy men whose natures sort with their vocations. -Francis Bacon,
> essayist, philosopher, and statesman (1561-1626)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to