So how do you get an OH II design criteria of .15/2000 using ECOH
sprinklers?  The K14.0 ECOH sprinklers I'm aware of are listed as standard
response when used in OH at a 20' x 20' spacing, so QR area reduction isn't
allowed.  When I look at Figure 11.2.3.1.1, I get .15/4000.  Am I missing
something?

Ed Kramer
Lawrence, KS

> Hello,
> 
> We have an existing system installed 20 x 20 with 14.5K ECOH sprinklers.
> They have now installed  a new wall separating the space into 2 spaces
> and left the sprinklers overspaced off the wall. The Calc plate
> indicates that the design was originally .15 fpm over 2,000 soft  and
> when we re-calc the system we are nearly identical to the results
> recorded on the data plate. If we calculate it at .20/1,500 it does not
> work.
> 
> Question is how to we even begin to sort this out in order to add a row
> of new heads to correct the overspacing? The new sprinklers all seem to
> be specifically listed for .20 (OH2) and i do not see a loophole to
> utilize a lower density and a larger Remote Area as in the original
> design. I also do not see an allowance in 13 for such a scenario
> (similar to the allowance for modifications to existing systems with
> residential heads that were originally designed for less than 7 psi end
> head pressure)
> 
> I do not think there will be any salvaging this system if we cannot
> reduce the density.
> 
> Thanks for any help,
> Greg