I need to design a sprinkler system, and I want to know if the
following will be "ok"

The hazard category per <FM> is HC2, distance that I have between 2
I-beans is 48.56'  (center to center) and the distance from the botton
of the I-beams are 47.57'. In HC2 the maximum distance is 12'. This
mean that if I use center to center I need 5 branch
(48.56/12=4.046)for sprinklers, but if I use the distance in the
botton of the I-bean, I need just 4.

Can I use 4 branches using the distances between the buttons of the I-Beam?

Regards