Nope - And by the way, NFPA 13 now specifically states that if a sprinkler is 
removed, it must be replaced with a new sprinkler.  If for some reason you 
remove the sprinkler, you must install a new one.

John

John August Denhardt, P.E., FSFPE
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES - Can you live without them?


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of ampeck
Sent: Friday, July 12, 2013 5:23 PM
To: [email protected]
Subject: Re: dry pnds off dry system

Ok yes but also after a dry system trip, test or actual activation, isn't all 
pendent heads supposed to be removed and any water drained? I can't locate it 
right now but it was something our field always did.

On Jul 13, 2013, at 3:01 AM, John Denhardt <[email protected]> wrote:

> Think about what you wrote.  If you tripped the system, the return bends 
> would not be able to be drained.  Return bends can only be used in an area 
> not subject to freezing,
> 
> John
> 
> John August Denhardt, P.E., FSFPE
> Strickland Fire Protection Incorporated
> 5113 Berwyn Road
> College Park, Maryland 20740
> Office Telephone Number:  301-474-1136
> Mobile Telephone Number:  301-343-1457
> FIRE SPRINKLERS SAVE LIVES - Can you live without them?
> 
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of ampeck
> Sent: Friday, July 12, 2013 11:55 AM
> To: [email protected]
> Subject: Re: dry pnds off dry system
> 
> Whether its a cooler or freezer if you're running a completely Dry System I 
> don't see a reason why you can use standard heads on return bends as in the 
> heated office.
> 
> And your right, save a control valve and separate main piping.
> 
> Correct me if I'm wrong but seems fine by me.
> 
> On Jul 12, 2013, at 10:38 PM, Matt Grise <[email protected]> wrote:
> 
>> I would be careful using a wet system even if it is called a "cooler". The 
>> evaporation coils can blow out air that is below freezing in order to get 
>> the whole cooler down to its target temp.
>> 
>> Also- just because they say they will keep it at 41 does not mean that they 
>> won't change their mind after it has been installed and dial it down.
>> 
>> Matt Grisé PE*, LEED AP, NICET II  
>> Sales Engineer 
>> Alliance Fire Protection 
>> 130 w 9th Ave.
>> North Kansas City, MO 64116
>> 
>> *Licensed in KS & MO 
>> 
>> 913.888.0647 ph 
>> 913.888.0618 f 
>> 913.927.0222 cell 
>> www. AFPsprink.com 
>> 
>> -----Original Message-----
>> From: [email protected] 
>> [mailto:[email protected]] On Behalf Of 
>> Martinez, Dewayne
>> Sent: Friday, July 12, 2013 10:34 AM
>> To: [email protected]
>> Subject: RE: dry pnds off dry system
>> 
>> The building footprint is 3800sf so I could eliminate a control valve
>> and a main by staying all dry.
>> 
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of
>> [email protected]
>> Sent: Friday, July 12, 2013 10:12 AM
>> To: [email protected]
>> Subject: RE: dry pnds off dry system
>> 
>> If it's a "cooler" and not subject to freezing you can put a wet system
>> in it.
>> 
>> Ron F
>> 
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of
>> Martinez, Dewayne
>> Sent: Friday, July 12, 2013 8:15 AM
>> To: [email protected]
>> Subject: dry pnds off dry system
>> 
>> I have a small building which has both unheated / heated spaces.  I am
>> going to run the entire building as a dry system with standard pnd heads
>> on return bends in the heated areas with ceilings.  There is a cooler in
>> the heated area that will need sprinkler protection in.  Can I still put
>> standard pnds on return bends (in the heated area) for the cooler or do
>> I need to drop dry pnds?
>> 
>> Thanks,
>> 
>> Dewayne   
>> 
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
>> .org
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
>> .org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to