Yes - new for 2013.

John August Denhardt, P.E., FSFPE
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES - Can you live without them?


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of ampeck
Sent: Friday, July 12, 2013 5:42 PM
To: [email protected]
Subject: Re: dry pnds off dry system

Is this a change in 2013? I have my new books sitting in the states but haven't 
been back to pick them up yet.


On Jul 13, 2013, at 4:34 AM, John Denhardt <[email protected]> wrote:

> Nope - And by the way, NFPA 13 now specifically states that if a sprinkler is 
> removed, it must be replaced with a new sprinkler.  If for some reason you 
> remove the sprinkler, you must install a new one.
> 
> John
> 
> John August Denhardt, P.E., FSFPE
> Strickland Fire Protection Incorporated
> 5113 Berwyn Road
> College Park, Maryland 20740
> Office Telephone Number:  301-474-1136
> Mobile Telephone Number:  301-343-1457
> FIRE SPRINKLERS SAVE LIVES - Can you live without them?
> 
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of ampeck
> Sent: Friday, July 12, 2013 5:23 PM
> To: [email protected]
> Subject: Re: dry pnds off dry system
> 
> Ok yes but also after a dry system trip, test or actual activation, isn't all 
> pendent heads supposed to be removed and any water drained? I can't locate it 
> right now but it was something our field always did.
> 
> On Jul 13, 2013, at 3:01 AM, John Denhardt <[email protected]> 
> wrote:
> 
>> Think about what you wrote.  If you tripped the system, the return bends 
>> would not be able to be drained.  Return bends can only be used in an area 
>> not subject to freezing,
>> 
>> John
>> 
>> John August Denhardt, P.E., FSFPE
>> Strickland Fire Protection Incorporated
>> 5113 Berwyn Road
>> College Park, Maryland 20740
>> Office Telephone Number:  301-474-1136
>> Mobile Telephone Number:  301-343-1457
>> FIRE SPRINKLERS SAVE LIVES - Can you live without them?
>> 
>> 
>> -----Original Message-----
>> From: [email protected] 
>> [mailto:[email protected]] On Behalf Of ampeck
>> Sent: Friday, July 12, 2013 11:55 AM
>> To: [email protected]
>> Subject: Re: dry pnds off dry system
>> 
>> Whether its a cooler or freezer if you're running a completely Dry System I 
>> don't see a reason why you can use standard heads on return bends as in the 
>> heated office.
>> 
>> And your right, save a control valve and separate main piping.
>> 
>> Correct me if I'm wrong but seems fine by me.
>> 
>> On Jul 12, 2013, at 10:38 PM, Matt Grise <[email protected]> wrote:
>> 
>>> I would be careful using a wet system even if it is called a "cooler". The 
>>> evaporation coils can blow out air that is below freezing in order to get 
>>> the whole cooler down to its target temp.
>>> 
>>> Also- just because they say they will keep it at 41 does not mean that they 
>>> won't change their mind after it has been installed and dial it down.
>>> 
>>> Matt Grisé PE*, LEED AP, NICET II  
>>> Sales Engineer 
>>> Alliance Fire Protection 
>>> 130 w 9th Ave.
>>> North Kansas City, MO 64116
>>> 
>>> *Licensed in KS & MO 
>>> 
>>> 913.888.0647 ph 
>>> 913.888.0618 f 
>>> 913.927.0222 cell 
>>> www. AFPsprink.com 
>>> 
>>> -----Original Message-----
>>> From: [email protected] 
>>> [mailto:[email protected]] On Behalf Of 
>>> Martinez, Dewayne
>>> Sent: Friday, July 12, 2013 10:34 AM
>>> To: [email protected]
>>> Subject: RE: dry pnds off dry system
>>> 
>>> The building footprint is 3800sf so I could eliminate a control valve
>>> and a main by staying all dry.
>>> 
>>> -----Original Message-----
>>> From: [email protected]
>>> [mailto:[email protected]] On Behalf Of
>>> [email protected]
>>> Sent: Friday, July 12, 2013 10:12 AM
>>> To: [email protected]
>>> Subject: RE: dry pnds off dry system
>>> 
>>> If it's a "cooler" and not subject to freezing you can put a wet system
>>> in it.
>>> 
>>> Ron F
>>> 
>>> -----Original Message-----
>>> From: [email protected]
>>> [mailto:[email protected]] On Behalf Of
>>> Martinez, Dewayne
>>> Sent: Friday, July 12, 2013 8:15 AM
>>> To: [email protected]
>>> Subject: dry pnds off dry system
>>> 
>>> I have a small building which has both unheated / heated spaces.  I am
>>> going to run the entire building as a dry system with standard pnd heads
>>> on return bends in the heated areas with ceilings.  There is a cooler in
>>> the heated area that will need sprinkler protection in.  Can I still put
>>> standard pnds on return bends (in the heated area) for the cooler or do
>>> I need to drop dry pnds?
>>> 
>>> Thanks,
>>> 
>>> Dewayne   
>>> 
>>> 
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
>>> .org
>>> 
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
>>> .org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> 
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to