Loaded question Dan.   The intent of the exception has to do with
unconditioned spaces that might be subject to freezing.   The TC did not
want to force an anti-freeze loop (touchy subject) or dry pipe system
into an otherwise wet residential application, based just on the
potential for freezing in selected compartments that are separated from
the dwelling unit and legitimately outside of the envelope. But the way
you word your question is open-ended.  Just because a compartment isn't
accessed from within a particular dwelling unit, doesn't mean it's
excepted if it's accessed from some other compartment that may not be
considered as "exterior" or on a balcony, breezeway, corridor, etc.   

So assuming it's a truly exterior compartment and separated without
openings to the dwelling unit as Pete alluded to, then yes.   But if
there's some other condition that isn't truly exterior, just because
it's not accessed from a dwelling unit doesn't arbitrarily exempt the
space from sprinkler protection.

The foregoing is my opinion only and does not necessarily represent the
opinion or intent of the NFPA Technical Committee on Residential
Sprinkler Systems.

Steve Leyton
Protection Design & Consulting
San Diego, CA


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dan
Adams
Sent: Tuesday, July 16, 2013 12:52 PM
To: [email protected]
Subject: NFPA 13R closet question

In NFPA 13R (2013) , paragraph 6.6.4 notes:

6.6.4* Sprinklers shall be installed in any closet used for heating or
air-conditioning equipment, washers, dryers, or water

heaters except as permitted by 6.6.7.

 

Paragraph 6.6.7 notes:

6.6.7 Sprinklers shall not be required in closets (regardless of size)
on exterior balconies and exterior breezeways/corridors,

regardless of size, as long as the closet does not have doors or
unprotected penetrations directly into the dwelling unit.

 

So, is it correct that an exterior closet which contains a furnace or
water heater doesn't require protection if the door to access the closet
is not located inside the unit ?  

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to