As DH noted this is what the AHJ wanted. AHJ's come in many flavors. The flavor 
that writes checks, also known as the Customer, has great authority to exceed 
minimum code. 

bv 

----- Original Message -----
From: "Dwight Havens" <[email protected]> 
To: [email protected] 
Sent: Tuesday, July 23, 2013 6:17:11 PM 
Subject: Re: SIGN for Backflow Prevention Assembly Forward Flow Test 

First, let me say that I do not believe that BFPA’s 
are really necessary to protect the public water supply for Class 1 and 2 fire 
protection systems. We won that battle 
twice in Arizona, but the water purveyors ultimately prevailed, so the war is 
over. Our concern is that these devices be 
as reliable as alarm check valves and not cause automatic sprinkler systems to 
fail. 

Tell me the utility of this information. It is nice to know but has no purpose. 
Like the main drain test, it is only of value 
if you have the previous tests to compare it to. 

Where does the system test flow rate come from and at what pressure? 
Remember those hydraulic calculations that had 
to be done to show the water supply was adequate to meet the system flow and 
pressure demands? It’s in there. 

Does that 
pressure compare to the upstream residual, the downstream residual? 
If the government requires you to analyze the data to determine if there is a 
problem, the upstream and downstream residuals need to be equal to or 
greater than the values shown in the hydraulic calculations at the design flow 
rate. The delta across the BFPA needs to 
be less than or equal to the value from the manufacturer’s literature at the 
design flow rate (hopefully the number used in the hydraulic calculations). If 
you flow more than the design flow rate, 
the delta should be compared to the manufacturer’s literature in order to 
evaluate the results. 

What does this tell me the main drain test does not? 
The main drain test (if compared to previous 
main drain tests) tells you whether or not the water supply to the system has 
changed over time. The forward flow test 
of the backflow prevention assembly is specifically looking at any changes in 
the operation of the BFPA. When 
performing the main drain test, you flow whatever the supply can provide 
through the fully opened valve. The 
forward flow test of the BFPA specifies a minimum flow rate, which makes 
comparing “apples to apples” more difficult if you are trying to look at the 
state of the water supply. You have to 
throttle the flow to the design flow rate for consistent results. 

The failure of a backflow device to "fully" open is not a 
nuanced phenomena. They barely flow or they flow "fully" relative to available 
pressure less friction loss. This was a problem in the early days of putting 
backflows designed for plumbing and process piping, constantly dynamic water 
systems, on sprinklers, primarily non-dynamic systems. Things would rust and 
rubbers would stick. Newer, sprinkler purposed models do not exhibit these 
failures as often. 

Yes, some makes and models were simply awful, 
but because of the testing, the ones that were bad were recognized and no 
longer accepted. New models have come 
along with much improved reliability, but no one has compiled the reliability 
data to convince the committee to eliminate or change the frequency of the 
test. For some reason, once a requirement is in the standard, it becomes much 
harder to remove it. 


The federal government is correct that the 
test, as presented in the standard, does not require relevant data be collected 
and compared to previous tests, which makes it a useless test. What is the 
pass/fail criteria? My assumption is that they are trying to correct this 
oversight, since they cannot waive the requirement. 


As the AHJ, they can raise the bar by requiring the information be provided on 
a sign and specifying how the data is to be collected and evaluated, by 
including the requirement in the contract language, or a referenced standard. 

Dwight 




________________________________ 
From: Ron Greenman <[email protected]> 
To: [email protected] 
Sent: Monday, July 22, 2013 9:17 PM 
Subject: Re: SIGN for Backflow Prevention Assembly Forward Flow Test 


Tell me the utility of this information. It is nice to know but has no 
purpose. Where dos the system test flow 
rate come from and at what pressure? Does that pressure compare to the 
upstream residual, the downstream residual? What does this tell me the main 
drain test does not? The failure of a backflow device to "fully" open is 
not a nuanced phenomena. They barely flow or they flow "fully" relative to 
available pressure less friction loss. This was a problem in the early days 
of putting backlows designed for plumbing and process piping, constantly 
dynamic water systems, on sprinklers, primarily non-dynamic systems. Things 
would rust and rubbers would stick. Newer, sprinkler purposed models do not 
exhibit these failures as often. But back to the sign. The information is 
nice, like the tach in my car. The car is automatic, shifting is controlled 
by the computer, and there is a rev limiter for when I shift it to the 
automatic manual mode I get information but it has value. Now I used to 
race motorcycles and my favorite had a very narrow rpm range (about 600). 
The tach was essential for optimum use of the gearbox whereas a speedometer 
would have been useless at best and a couple extra pounds of detriment. 
That speedo in my car though gives me info that helps me avoid a ticket. 


On Mon, Jul 22, 2013 at 5:15 PM, Dwight Havens <[email protected]>wrote: 

> Why is this information useless? The point of the forward flow test is to 
> ensure that the backflow device is opening properly. Like the main drain 
> test, the information is only properly assessed when compared to previous 
> tests. Initial system configuration (tests) are often documented at 
> acceptance, but rarely kept in a place where the information is available 
> in the field. This is one of the areas that is covered in the standard, in 
> which case the AHJ and the owner have every right to make the requirement 
> to facilitate proper assessment of the water supply to the system over time. 
> 
> 
> 
> 
> ________________________________ 
> From: Ron Greenman <[email protected]> 
> To: [email protected] 
> Sent: Monday, July 22, 2013 7:16 PM 
> Subject: Re: SIGN for Backflow Prevention Assembly Forward Flow Test 
> 
> 
> And apart from the uselessness of this information they want it because 
> they want it. I'd certainly like nonsense like this to be justified. I 
> certainly hope the request for this "extra" was clearly specified in the 
> bidding documents and that you were able to add the few dollars this will 
> cost accordingly. 
> 
> 
> On Mon, Jul 22, 2013 at 1:57 PM, Bobby Gillett <[email protected] 
> >wrote: 
> 
> > Brad, 
> > 
> > Your suggestion/question makes sense, however, this is a military base 
> and 
> > they are calling for this info recorded on a metal placard and placed on 
> > the backflow, for sure. 
> > 
> > Thank you. 
> > 
> > 
> > On Mon, Jul 22, 2013 at 3:34 PM, Brad Casterline < 
> [email protected] 
> > >wrote: 
> > 
> > > Just curious Bobby-- would this sign be for initial acceptance? It 
> seems 
> > > more practical to require similar to Main Drain Test tags- because 
> there 
> > > might be slight variations from test to test, and the metal one might 
> be 
> > > scrap metal down the road! 
> > > 
> > > -----Original Message----- 
> > > From: Bobby Gillett [mailto:[email protected]] 
> > > Sent: Monday, July 22, 2013 3:14 PM 
> > > To: [email protected] 
> > > Subject: Re: SIGN for Backflow Prevention Assembly Forward Flow Test 
> > > 
> > > Thank you Forest, as I mentioned before - We can make a sign, just 
> hoping 
> > > there were already some out there - looks more professional.... 
> > > 
> > > 
> > > On Mon, Jul 22, 2013 at 3:12 PM, Forest Wilson <[email protected] 
> > > >wrote: 
> > > 
> > > > Can you just make a sign using the back of a hydraulic call sign and 
> > > > permanent marker? 
> > > > 
> > > > Sent from my iPhone 
> > > > 
> > > > On Jul 22, 2013, at 4:04 PM, Bobby Gillett <[email protected]> 
> > > > wrote: 
> > > > 
> > > > > We have a project where the spec's are calling for us to install a 
> > > metal 
> > > > > placard on the backflow assembly with the pressure readings 
> upstream 
> > > and 
> > > > > downstream of the assembly, total pressure drop and the system test 
> > > flow 
> > > > > rate. 
> > > > > 
> > > > > Has anyone had to supply similar signs and know where we can get 
> > such a 
> > > > > sign? We could have some made, but why reinvent the wheel if you 
> > don't 
> > > > have 
> > > > > too? 
> > > > > 
> > > > > Thank you for your assistance in advance. 
> > > > > 
> > > > > Bobby Gillett 
> > > > > Living Water Fire Protection, LLC 
> > > > > (850) 937-1850 
> > > > > _______________________________________________ 
> > > > > Sprinklerforum mailing list 
> > > > > [email protected] 
> > > > > 
> > > > 
> > > 
> > > 
> > 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
> > > > _______________________________________________ 
> > > > Sprinklerforum mailing list 
> > > > [email protected] 
> > > > 
> > > > 
> > > 
> > > 
> > 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
> > > > 
> > > _______________________________________________ 
> > > Sprinklerforum mailing list 
> > > [email protected] 
> > > 
> > > 
> > 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
> > > 
> > > _______________________________________________ 
> > > Sprinklerforum mailing list 
> > > [email protected] 
> > > 
> > > 
> > 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
> > > 
> > _______________________________________________ 
> > Sprinklerforum mailing list 
> > [email protected] 
> > 
> > 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
> > 
> 
> 
> 
> -- 
> Ron Greenman 
> Instructor 
> Fire Protection Engineering Technology 
> Bates Technical College 
> 1101 So. Yakima Ave. 
> Tacoma, WA 98405 
> 
> [email protected] 
> 
> http://www.bates.ctc.edu/fireprotection/ 
> 
> 253.680.7346 
> 253.576.9700 (cell) 
> 
> Member: 
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC 
> 
> They are happy men whose natures sort with their vocations. -Francis Bacon, 
> essayist, philosopher, and statesman (1561-1626) 
> _______________________________________________ 
> Sprinklerforum mailing list 
> [email protected] 
> 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
> _______________________________________________ 
> Sprinklerforum mailing list 
> [email protected] 
> 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
> 



-- 
Ron Greenman 
Instructor 
Fire Protection Engineering Technology 
Bates Technical College 
1101 So. Yakima Ave. 
Tacoma, WA 98405 

[email protected] 

http://www.bates.ctc.edu/fireprotection/ 

253.680.7346 
253.576.9700 (cell) 

Member: 
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC 

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626) 
_______________________________________________ 
Sprinklerforum mailing list 
[email protected] 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
_______________________________________________ 