Why cant we just use the hydraulic data plate for the demand needed and add
a line for maximum pressure loss allowed through backflow and leave it at
that? Then if the backflow is replaced there is a number to work to and you
know how much flow is needed if it is measured.



On Fri, Jul 26, 2013 at 5:34 PM, John Denhardt <[email protected]
> wrote:

> Sounds like a good opportunity for a public input.
>
> Sent from my Motorola Smartphone on the Now Network from Sprint!
>
>
> -----Original message-----
> From: Dwight Havens <[email protected]>
> To: "[email protected]" <
> [email protected]>
> Sent: Fri, Jul 26, 2013 17:57:21 EDT
> Subject: Re: SIGN for Backflow Prevention Assembly Forward Flow Test
>
> Then they ought to say that in the code language.
>
> Dwight
>
>
>
>
> ________________________________
> From: John Denhardt <[email protected]>
> To: "[email protected]" <
> [email protected]>
> Sent: Thursday, July 25, 2013 3:07 PM
> Subject: RE: SIGN for Backflow Prevention Assembly Forward Flow Test
>
>
> While I do disagree to some extent of what the NFPA 25 committee has done,
> Roland statement is correct.  I have had numerous discussions with NFPA 25
> committee members where they have stated the intent was to exercise the
> device at near system demand.  The key word to me was "Exercise".
>
> John
>
> John August Denhardt, P.E., FSFPE
> Strickland Fire Protection Incorporated
> 5113 Berwyn Road
> College Park, Maryland 20740
> Office Telephone Number:  301-474-1136
> Mobile Telephone Number:  301-343-1457
> FIRE SPRINKLERS SAVE LIVES - Can you live without them?
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Forest Wilson
> Sent: Thursday, July 25, 2013 2:42 PM
> To: [email protected]
> Subject: Re: SIGN for Backflow Prevention Assembly Forward Flow Test
>
> Here is an email on this topic that Roland addressed in the past:
>
> Im not going to say it was one of those casual assumptions that all
> systems are calculated nor that all risers have placards.  The main
> thing to keep in mind that the intent is simply to fully EXERCISE the
> BFP at what os expected to be the system demand.  If no data
> available, a discussion with the AHJ is warranted.  As for benchmarks,
> only the flow is pertinent and pressure is irrelevant.
>
> Roland
>
> On Dec 22, 2009, at 2:44 PM, Matthew J. Willis wrote:
>
> >>
> >> On a more important matter: If a system was retrofitted with a
> >> backflow,
> > and
> >> there is no hydraulic calc plaque attached to the riser, and NFPA
> >> requires
> >> forward flow testing of backflows, how can you conduct the test
> >> without a
> >> benchmark to test against?
> >>
> >> What is the recommended practice in this scenario?
> >> Forest Wilson
>
> Sent from my iPhone
>
> On Jul 25, 2013, at 12:16 PM, Ron Greenman <[email protected]> wrote:
>
> > Then subjective good flow demonstrates a working valve? If so all the
> > numbers bantered around are pretty meaningless.
> >
> >
> >
> > On Thu, Jul 25, 2013 at 8:07 AM, Forest Wilson <[email protected]
> >wrote:
> >
> >> No.
> >> The intent is not to pitot the output but to exercise the valve.
> >>
> >>
> >> Sent from my iPhone
> >>
> >> On Jul 25, 2013, at 10:56 AM, Ron Greenman <[email protected]>
> wrote:
> >>
> >>> Forest. What were you flowing to discover these failures? Main drain or
> >>> some special test header? Would a sign with the data requested by the
> >>> customer that started this thread have had any utility in helping you
> >>> discover the problem?
> >>>
> >>> Then back to that perennial question of what's a "full flow " test and
> >> how
> >>> do you do one? I think Roland said the intent was to flow an equivalent
> >> to
> >>> the design discharge criteria. How do you do this? Do we run a pitot
> >>> somewhere on the system? Do we catch and measure discharge? If so, from
> >>> where? How do we arrange the test port(s)? Do we flow the design area
> or
> >>> simulate it elsewhere? Do we need results of at least or better flow or
> >>> right on the money flow? If not either of those how do we judge?
> >>>
> >>> Doesn't the hydraulic data plate note the required psi per the calcs at
> >> the
> >>> BOR and the static? Isn't the difference the residual drop at that
> point
> >>> relative to the design area? Wouldn't a main drain with good flow at a
> >> psi
> >>> around the BOR rating, and returning to close to the noted static when
> >>> terminated suggest a fully open valve, or an adequately open valve if
> the
> >>> UG is oversized? In the latter case the partially open valve is
> >> equivalent
> >>> to fully open for the system I just described. Am I missing something
> >> here?
> >>> An erroneous a priori? My understanding of hydraulics wrong? Main
> drains
> >>> are too small to simulate the result of all design area heads flowing
> as
> >>> the water passes through the BOR?
> >>>
> >>>
> >>> On Thu, Jul 25, 2013 at 7:34 AM, Forest Wilson <[email protected]
> >>> wrote:
> >>>
> >>>> I still have the check valve from a Ames that failed to open.
> >>>> It was jammed shut, discovered when I was called out because they
> >> couldn't
> >>>> do the fire pump test.
> >>>>
> >>>> In another case, I tested a backflow and it failed (on a Best Buy
> >> store).
> >>>> I opened the valve up and the check was
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852