NFPA 13 final did more than simply say a means shall be provided. The CMTC now says Indicate the means and state whether the when opened did it create the system flow demand.
I also submitted a PI allowing the main drain to be larger than 2 inches so it can provide the means on higher flow systems. A literal interpretation of 13 allows no ore than a 2 inch main drain. Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org On Aug 1, 2013, at 1:20 AM, "Douglas Hicks" <[email protected]> wrote: > > So after 15 years, there is still lots of confusion about the forward flow > and provision to do a forward flow test is still lacking in new systems. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org