I used to carry 1 1/4 and 2 inch 45's, 6-inch nipples and 2 foot piece of pipe 
threaded on one end, along with my pitot, just so I could take such 
measurements of the main drains.

Dwight




________________________________
 From: Ron Greenman <[email protected]>
To: [email protected] 
Sent: Monday, July 29, 2013 5:18 PM
Subject: Re: SIGN for Backflow Prevention Assembly Forward Flow Test
 

This is kind of like the story where a guy in a bar asks the shapely young
thing on the next barstool if she'd sleep with him for $100,000.00. She
answers with an enthusiastic yes. He then asks if she'd sleep with him for
$10.00. Her response is an indignant, "what do you take me for, a whore?"
His reply is, "we've already established that. Now we're just negotiating
price."

This was an illustrative metaphor Steve, not a dirty joke.

We've established that a forward flow is required. And surprisingly we've
actually got a fairly definitive description of what we're testing for by
the committee in the next edition. To me it's in two parts though. First
we're not testing so much as "exercising" a component, which to me is a
maintenance issue. In the process though we're also testing as we're
determining if said component is working. But when you do a "test" you need
a standard of performance. That brings us to part 2 and that standard
appears to be "at system demand." That requires a measurement for
verification and the comparative baseline standard. So, and to me only,
this new language is as convoluted as the old and doesn't give me a clear
directive. Am I exercising or comparing results, or both? Can I say that a
15 head design, using nominal 1/2 inch orifices has a total surface area of
2.94 square inches and a nominal 2 inch main drain has a surface area of
3.14 square inches so I'll easily flow as much through my 2 inch main drain
as system demand? Or do I have to calculate BOR flow demand, test and
measure (pitot or buckey) for flow there at acceptance for verification,
and then do that same procedure each year for confirmation? Or can I just
see a good stream from the main drain, note the pressure are consistent
with the acceptance test and say,"That there no backlow thingie is workin'
just fine."?


On Mon, Jul 29, 2013 at 1:57 PM, Mark A. Sornsin, P.E. <
[email protected]> wrote:

> Depends on the edition of the standard a local jurisdiction has adopted,
> as well as any local amendments - but yes, forward flow tests of the
> backflow assembly are required by NFPA 13 and 25.
>
> Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
> Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
> http://www.kfiengineers.com
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of
> [email protected]
> Sent: Monday, July 29, 2013 3:49 PM
> To: [email protected]
> Subject: Re: SIGN for Backflow Prevention Assembly Forward Flow Test
>
> Is this "forward flow test" now part of the required code? I was just on a
> job the other day. New Construction. I noticed that all the systems had a
> setup  with (2) 2 1/2" hose valves after the backflow and alarm valve, in
> addition to  the 2" main drain. I take it that these 2 1/2's are for this
> test?
>
>
> In a message dated 7/29/2013 3:57:24 P.M. Eastern Daylight Time,
> [email protected] writes:
>
> That  isn't what the intent of the code is as stated.....just flow at
> system demand. I can only speak for us, but we do a LOT of risers with only
>  a 250 gpm or so demand...sometimes even less.
>
> A 4" drain is well  over what we need to open it up enough for system
> demand. I would bet a 2"  drain gets really close.
>
>
> On Mon, Jul 29, 2013 at 2:52 PM, David  Autry <[email protected]> wrote:
>
> > Wouldn't it be easier, if  you have a 4" backflow preventer you run 4"
> > out the wall, 3" BFP, 3"  out the wall, etc...
> > That should open her up all the  way.
> >
> >
> > David Autry
> >
> > Meininger Fire  Protection Inc.
> > 2521 W L St. Suite No.4
> > Lincoln, Ne  68522
> > Voice (402) 466-2616
> > Fax (402) 466-2617
> >  [email protected]
> >
> > -----Original Message-----
> > From:  [email protected]
> >  [mailto:[email protected]] On Behalf Of
> Greg
> > McGahan
> > Sent: Monday, July 29, 2013 2:35 PM
> > To:  [email protected]
> > Subject: Re: SIGN for Backflow  Prevention Assembly Forward Flow Test
> >
> > What would be simple and  helpful would be a table similar to the one
> > used for sizing fire pump  Suction/Discharge/Relief Valve Piping etc.
> >
> > Since you are not  measuring pressure, you could say 2" up to X
> > gallons, 2.5" for Y  etc....
> >
> > A 2-1/2" Main drain is much easier and cheaper than  some of the
> > arrangments left / required on backflow  preventers.
> >
> > Greg
> >
> >
> > On Mon, Jul 29, 2013  at 12:46 PM, Ron Greenman
> >  <[email protected]>wrote:
> >
> > > Better but it is  still interpretable as requiring a measured flow
> > > be established  (if using the main drain location then the BOR
> > > design
> data).
> > > Then  you'd need a port that flowed that much, main drain or
> > > otherwise,  and then measure your annual test against anticipated
> > > flow to make
> >  > sure you are meeting or exceeding the required flow. Or am I
> > missing
> > > something? I'm pretty certain that newer fire service  rated
> > > backflows don't fail any more often than normal FS checks,  and that
> > > that type of failure is either catastrophic (doesn't  open or barely
> > > opens) wouldn't a simple main drain test with  decent flow
> > > demonstrate that the valve is working? just a Forum  question as
> > > this is a done deal and I wasn't invited to join the  exclusive
> > > 25 club.
> > >
> > >
> > > On Mon,  Jul 29, 2013 at 7:11 AM, Roland Huggins
> > >  <[email protected]>wrote:
> > >
> > > > the  next edition has been cleaned-up on this issue.
> > > >
> > >  > _______________________________________________________________
> >  > > 25-271
> > > Log
> > > > #CP15 Final Action:  Accept
> > > > (13.6.2.1, 13.6.2.2 (New))
> > > >  _______________________________________________________________
> > >  Submitter:
> > > > Technical Committee on Inspection, Testing, and  Maintenance of
> > > Water-Based
> > > > Systems,
> >  > >
> > > > Recommendation: Revise 13.6.2.1 to read as  follows:
> > > > 13.6.2.1 All backflow preventers installed in fire  protection
> > > > system piping shall be exercised annually by  conducting a forward
> > > > flow test at a minimum flow rate of the  system design.
> > > > Add new 13.6.2.2 and renumber subsequent  sections accordingly:
> > > > 13.6.2.2 Where hydrants or inside hose  stations are located
> > > > downstream of the backflow preventer,  the forward flow test shall
> > > > include hose stream demand.  Substantiation: This change was
> > > > needed to better reflect  that the backflow preventer is not a
> > > > precise test whereby  the flow through it must be measured but
> > > > effort to exercise  the device at flows as near as
> > > possible
> > > > to the  system demand.
> > > > Committee Meeting Action: Accept
> > >  > Number Eligible to Vote: 33
> > > > Ballot Results:  Affirmative: 32 Negative: 1 Explanation of Negative:
> > > >
> >  > > RAY, R.: This proposal should have been accepted in principle:
> > the
> > > wording
> > > > "at a minimum flow rate" is  confusing and should be reworded.
> > > >  _______________________________________________________________
> > >  > 25-272
> > > Log
> > > > #121 Final Action:  Accept
> > > >
> > > > (13.6.2.1.1)
> > >  >
> > > >  _______________________________________________________________
> > >  Submitter:
> > > > Roland J. Huggins, American Fire Sprinkler  Association, Inc.
> > > > Recommendation: Delete the following  text:
> > > >
> > > > 13.6.2.1.1 For backflow preventers  sized 2 in. (50 mm) and under,
> > > > the forward flow test shall  be acceptable to conduct without
> > > > measuring flow, where the  test outlet is of a size to flow the
> > > > system
> > demand.
> > > >  Substantiation: This section implies that a measured flow is
> > > > required for Backflow preventers (BFP) larger than 2 in when
> > > > nothing
> >  > > in 13.6.2.1
> > > states
> > > > such a  requirement. There are other means to identify that the
> > > > system demand is flowing through the BFP as discussed in
> > > > A.13.6.2.1
> >  > > It also
> > > needs
> > > > to be kept in mind that  we are simply exercising the BFP to
> > > > ensure it
> > >  will
> > > > fully open at approximately the system demand. A high  degree of
> > > > accuracy regarding the volume of water is not  warranted.
> > > > Additionally, BFP's are subjected to an annual  internal
> > > > inspection as part of the cross
> > >  connection
> > > > protection program. Committee Meeting Action:  Accept Number
> > > > Eligible to Vote: 33 Ballot Results:  Affirmative: 33
> > > >
> > > >
> > > >
> >  > > Roland Huggins, PE - VP Engineering
> > > >
> > >  > American Fire Sprinkler Assn.       ---     Fire Sprinklers Saves
> > Lives
> > > > Dallas,  TX
> > > > http://www.firesprinkler.org
> > > >
> >  > >
> > > >
> > > >
> > > >
> > >  > On Jul 26, 2013, at 2:57 PM, Dwight Havens
> > > <[email protected]>
> > > wrote:
> > > >
> >  > > > Then they ought to say that in the code language.
> > >  > >
> > > > > Dwight
> > > > >
> > >  > >
> > > > >
> > > > >
> > > > >  ________________________________
> > > > > From: John Denhardt  <[email protected]>
> > > > > To:  "[email protected]" <
> > > >  [email protected]>
> > > > > Sent:  Thursday, July 25, 2013 3:07 PM
> > > > > Subject: RE: SIGN for  Backflow Prevention Assembly Forward Flow
> > > > > Test
> >  > > >
> > > > >
> > > > > While I do  disagree to some extent of what the NFPA 25
> > > > > committee  has
> > > > done, Roland statement is correct.  I have had  numerous
> > > > discussions with NFPA 25 committee members where  they have stated
> > > > the intent was to
> > >  exercise
> > > > the device at near system demand.  The key  word to me was
> "Exercise".
> > > > >
> > > > >  John
> > > > >
> > > > > John August Denhardt, P.E.,  FSFPE Strickland Fire Protection
> > > > > Incorporated
> >  > > > 5113 Berwyn Road
> > > > > College Park, Maryland  20740
> > > > > Office Telephone Number:  301-474-1136  Mobile Telephone Number:
> > > > > 301-343-1457 FIRE SPRINKLERS  SAVE LIVES - Can you live without
> > > > > them?
> > >  > >
> > > > > -----Original Message-----
> > > >  > From: [email protected] [mailto:
> >  > > [email protected]] On Behalf Of
> > Forest
> > > Wilson
> > > > > Sent: Thursday, July 25,  2013 2:42 PM
> > > > > To:  [email protected]
> > > > > Subject: Re:  SIGN for Backflow Prevention Assembly Forward Flow
> > > > > Test
> > > > >
> > > > > Here is an email on this  topic that Roland addressed in the past:
> > > > >
> > >  > > Im not going to say it was one of those casual assumptions
> > > that
> > > > > all systems are calculated nor that all risers  have placards.
> > > > > The main thing to keep in mind  that the intent is simply to
> > > > > fully EXERCISE the BFP at  what os expected to be the system
> > > > > demand.  If no  data available, a discussion with the AHJ is
> > > > > warranted.  As for
> >  > > > benchmarks, only the flow is pertinent and pressure is
>  irrelevant.
> > > > >
> > > > > Roland
> > >  > >
> > > > > On Dec 22, 2009, at 2:44 PM, Matthew J.  Willis wrote:
> > > > >
> > > > >>>
> >  > > >>> On a more important matter: If a system was retrofitted  with
> > a
> > > > >>> backflow,
> > > > >>  and
> > > > >>> there is no hydraulic calc plaque attached  to the riser, and
> > > > >>> NFPA requires forward flow  testing of backflows, how can you
> > > > >>> conduct the  test without a benchmark to test against?
> > > >  >>>
> > > > >>> What is the recommended practice  in this scenario?
> > > > >>> Forest Wilson
> > >  > >
> > > > > Sent from my iPhone
> > > >  >
> > > > > On Jul 25, 2013, at 12:16 PM, Ron Greenman
> > > > > <[email protected]>
> > > > wrote:
> > > >  >
> > > > >> Then subjective good flow demonstrates a  working valve? If so
> > > > >> all the numbers bantered  around are pretty meaningless.
> > > > >>
> > > >  >>
> > > > >>
> > > > >> On Thu, Jul 25,  2013 at 8:07 AM, Forest Wilson
> > > > >> <[email protected]
> > > > >wrote:
> > > >  >>
> > > > >>> No.
> > > > >>> The  intent is not to pitot the output but to exercise the valve.
> > > >  >>>
> > > > >>>
> > > > >>>  Sent from my iPhone
> > > > >>>
> > > >  >>> On Jul 25, 2013, at 10:56 AM, Ron Greenman  >>>
> > > > <[email protected]>
> > > > wrote:
> >  > > >>>
> > > > >>>> Forest. What were  you flowing to discover these failures?
> > > > >>>> Main
> > > >  >>>> drain
> > > > or
> > > > >>>>  some special test header? Would a sign with the data
> > > > >>>> requested
> > >  > >>>> by
> > > the
> > > > >>>>  customer that started this thread have had any utility in
> > > >  >>>> helping
> > > you
> > > > >>>>  discover the problem?
> > > > >>>>
> > > >  >>>> Then back to that perennial question of what's a "full flow  "
> > > > >>>> test
> > > and
> > > >  >>> how
> > > > >>>> do you do one? I think  Roland said the intent was to flow an
> > > > equivalent
> >  > > >>> to
> > > > >>>> the design  discharge criteria. How do you do this? Do we run
> > > > >>>> a
> > > >  >>>> pitot somewhere on the system? Do we catch and  measure
> > > > >>>> discharge? If so,
> > > >  from
> > > > >>>> where? How do we arrange the test  port(s)? Do we flow the
> > > > >>>> design
> > >  area
> > > > or
> > > > >>>> simulate it  elsewhere? Do we need results of at least or
> > > > >>>> better
> > > >  >>>> flow
> > > > or
> > > > >>>>  right on the money flow? If not either of those how do we
> judge?
> > >  > >>>>
> > > > >>>> Doesn't the hydraulic  data plate note the required psi per
> > > > >>>> the  calcs
> > > > at
> > > > >>> the
> > >  > >>>> BOR and the static? Isn't the difference the residual  drop
> > > at
> > > > >>>> that
> > > >  point
> > > > >>>> relative to the design area? Wouldn't  a main drain with good
> > > > >>>> flow
> > > at  a
> > > > >>> psi
> > > > >>>> around  the BOR rating, and returning to close to the noted
> > > >  >>>> static
> > > when
> > > > >>>>  terminated suggest a fully open valve, or an adequately open
> > > >  >>>> valve
> > > if
> > > > the
> > > >  >>>> UG is oversized? In the latter case the partially open valve
> > > > is
> > > > >>> equivalent
> > > >  >>>> to fully open for the system I just described. Am I  missing
> > > something
> > > > >>> here?
> >  > > >>>> An erroneous a priori? My understanding of  hydraulics wrong?
> > > > >>>> Main
> > > >  drains
> > > > >>>> are too small to simulate the result  of all design area
> > > > >>>> heads
> > > flowing
> > > > as
> >  > > >>>> the water passes through the BOR?
> > > >  >>>>
> > > > >>>>
> > > >  >>>> On Thu, Jul 25, 2013 at 7:34 AM, Forest Wilson <
> >  > [email protected]
> > > > >>>> wrote:
> >  > > >>>>
> > > > >>>>> I still have  the check valve from a Ames that failed to open.
> > > >  >>>>> It was jammed shut, discovered when I was called out
> > > > because
> > > > >>>>> they
> > > >  >>> couldn't
> > > > >>>>> do the fire pump  test.
> > > > >>>>>
> > > >  >>>>> In another case, I tested a backflow and it failed (on a
> > > > Best
> > > > >>>>> Buy
> > > > >>>  store).
> > > > >>>>> I opened the valve up and the  check was damaged, would only
> > > > >>>>> open  a
> > > > >>> third.
> > > >  >>>>>
> > > > >>>>>
> > > >  >>>>>
> > > > >>>>> Sent from my  iPhone
> > > > >>>>>
> > > >  >>>>> On Jul 24, 2013, at 8:53 PM, Ron Greenman
> > >  > >>>>> <[email protected]>
> > > >  >>> wrote:
> > > > >>>>>
> > > >  >>>>>> Worked well for plumbing and process piping  applications
> > > > as
> > > > >>>>>> they
> > >  are
> > > > >>>>>> constantly being  exercised.
> > > > >>>>>>
> > > >  >>>>>>
> > > > >>>>>> On Wed,  Jul 24, 2013 at 5:12 PM, Dwight Havens <
> > > >  [email protected]
> > > > >>>>>>  wrote:
> > > > >>>>>>
> > > >  >>>>>>> I do remember the ones with the rods in the  center of
> > > > the
> > > > >>>>>>> valve
> >  > > being
> > > > >>>>>>> particularly  poor.
> > > > >>>>>>>
> > > >  >>>>>>> Dwight
> > > >  >>>>>>>
> > > >  >>>>>>>
> > > >  >>>>>>>
> > > >  >>>>>>>
> > > > >>>>>>>  ________________________________
> > > >  >>>>>>> From: Ron Greenman  <[email protected]>
> > > > >>>>>>>  To: [email protected]
> > > >  >>>>>>> Sent: Tuesday, July 23, 2013 11:25 PM
> >  > > >>>>>>> Subject: Re: SIGN for Backflow  Prevention Assembly
> > Forward
> > > > >>>>>>>  Flow
> > > > Test
> > > >  >>>>>>>
> > > >  >>>>>>>
> > > > >>>>>>> By  the mid-nineties you have the early Ames models
> > > > >>>>>>> purpose
> > > >  >>>>>>> built
> > > > for
> > > >  >>>>>>> sprinklers readily available, but many units  being
> > > > installed
> > > > >>>>>>> are
> >  > > still
> > > > >>>>> not
> > > >  >>>>>>> listed for fire service as many jurisdictions  don't
> > > > consider
> > > > >>>>>>> the
> > >  > fire
> > > > >>>>> line
> > > >  >>>>>>> a fire line until after the backflow, and a n  on-listed
> > > > >>>>>>> device is
> >  > > >>>>> cheaper
> > > >  >>>>>>> than a listed one. Plus many go back to the  seventies
> > > > and
> > > > >>>>>>> many
> > >  used
> > > > >>>>> weights
> > > >  >>>>>>> instead of springs and complicated lever systems  for
> > > > joining
> > > > >>>>>>> the
> > >  > >>>>> clappers
> > > >  >>>>>>> and weights. Wish I could post a picture.
> >  > > >>>>>>>
> > > >  >>>>>>>
> > > > >>>>>>> On  Tue, Jul 23, 2013 at 7:33 PM, Dwight Havens <
> > > >  [email protected]
> > > > >>>>>>>>  wrote:
> > > > >>>>>>>
> > > >  >>>>>>>> Give me a time frame. My best recollection is  the mid
> '90's.
> > > > >>>>>>>>
> > >  > >>>>>>>> Dwight
> > > >  >>>>>>>>
> > > >  >>>>>>>>
> > > >  >>>>>>>>
> > > >  >>>>>>>>
> > > >  >>>>>>>> ________________________________
> > >  > >>>>>>>> From: Ron Greenman  <[email protected]>
> > > >  >>>>>>>> To:  [email protected]
> > > >  >>>>>>>> Sent: Tuesday, July 23, 2013 9:12 PM
> >  > > >>>>>>>> Subject: Re: SIGN for Backflow  Prevention Assembly
> > Forward
> > > > >>>>>>>>  Flow
> > > > Test
> > > >  >>>>>>>>
> > > >  >>>>>>>>
> > > >  >>>>>>>> Were these the plumbing type before fire  service listed
> > > > >>>>>>>>  devices
> > > > >>>>> existed.
> > > >  >>>>>>>>
> > > >  >>>>>>>>
> > > >  >>>>>>>> On Tue, Jul 23, 2013 at 4:32 PM, Dwight  Havens <
> > > > >>> [email protected]
> > >  > >>>>>>>>> wrote:
> > > >  >>>>>>>>
> > > >  >>>>>>>>> Yes, yes, and yes.  The original  proposal was based on
> > > > >>>>>>>>>  observed
> > > > >>>>>>> failures
> > >  > >>>>>>>>> of BFPAs to operate properly during  main drain testing.
> > > >  >>>>>>>>>
> > > >  >>>>>>>>> Glendale, AZ public library specifically  comes to mind.
> > > > >>>>>>>>>
> >  > > >>>>>>>>> Dwight
> > > >  >>>>>>>>>
> > > >  >>>>>>>>>
> > > >  >>>>>>>>>
> > > >  >>>>>>>>>
> > > >  >>>>>>>>> ________________________________
> >  > > >>>>>>>>> From: Todd Williams  <[email protected]>
> > > > >>>>>>>>>  To: "[email protected]" <
> > > >  >>>>>>>>>  [email protected]>
> > > >  >>>>>>>>> Sent: Monday, July 22, 2013 9:32  PM
> > > > >>>>>>>>> Subject: Re: SIGN  for Backflow Prevention Assembly
> > > > >>>>>>>>> Forward
> > > >  >>>>>>>>> Flow
> > > > Test
> > >  > >>>>>>>>>
> > > >  >>>>>>>>>
> > > >  >>>>>>>>> Has there ever been an instance of system  failure due
> > > > to
> > > > >>>>>>>>>  the
> > > > >>> backflow
> > > >  >>>>>>> not
> > > >  >>>>>>>>> properly opening? How about detection of  a BFP problem
> > > > >>>>>>>>> during  a
> > > > full
> > > > >>>>>>>  flow
> > > > >>>>>>>>> test. How about  something subsequent to the initial
> > acceptance?
> > > >  >>>>>>>>>
> > > >  >>>>>>>>> Todd G Williams, PE
> > > >  >>>>>>>>> Fire Protection Design/Consulting  Stonington, CT
> > > > >>>>>>>>>  860-535-2080
> > > > >>>>>>>>>  www.fpdc.com
> > > > >>>>>>>>>
> >  > > >>>>>>>>>  _______________________________________________
> > > >  >>>>>>>>> Sprinklerforum mailing list
> > >  > >>>>>>>>>  [email protected]
> > > >  >>>>>>>>>
> > > >  >>>>>>>>>
> > > >  >>>>>>>>
> > > >  >>>>>>>
> > > > >>>>>
> >  > > >>>
> > > >
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > > kl
> >  > er.org
> > > > >>>>>>>>>  _______________________________________________
> > > >  >>>>>>>>> Sprinklerforum mailing list
> > >  > >>>>>>>>>  [email protected]
> > > >  >>>>>>>>>
> > > >  >>>>>>>>>
> > > >  >>>>>>>>
> > > >  >>>>>>>
> > > > >>>>>
> >  > > >>>
> > > >
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > > kl
> >  > er.org
> > > > >>>>>>>>>
> >  > > >>>>>>>>
> > > >  >>>>>>>>
> > > >  >>>>>>>>
> > > >  >>>>>>>> --
> > > >  >>>>>>>> Ron Greenman
> > > >  >>>>>>>> Instructor
> > > >  >>>>>>>> Fire Protection Engineering Technology Bates  Technical
> > > > >>>>>>>> College
> >  > > >>>>>>>> 1101 So. Yakima Ave.
> > >  > >>>>>>>> Tacoma, WA 98405
> > > >  >>>>>>>>
> > > >  >>>>>>>> [email protected]
> > > >  >>>>>>>>
> > > >  >>>>>>>>  http://www.bates.ctc.edu/fireprotection/
> > > >  >>>>>>>>
> > > >  >>>>>>>> 253.680.7346
> > > >  >>>>>>>> 253.576.9700 (cell)
> > > >  >>>>>>>>
> > > >  >>>>>>>> Member:
> > > >  >>>>>>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA,  NIBS, WSAFM,
> > > > >>>>>>>> WFC,
> >  > WFSC
> > > > >>>>>>>>
> > > >  >>>>>>>> They are happy men whose natures sort with  their
> vocations.
> > > > -Francis
> > > >  >>>>>>> Bacon,
> > > >  >>>>>>>> essayist, philosopher, and statesman  (1561-1626)
> > > > >>>>>>>>  _______________________________________________
> > > >  >>>>>>>> Sprinklerforum mailing list  >>>>>>>>
> > > > [email protected]
> > > >  >>>>>>>>
> > > >  >>>>>>>>
> > > >  >>>>>>>
> > > > >>>>>
> >  > > >>>
> > > >
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > > kl
> >  > er.org
> > > > >>>>>>>>  _______________________________________________
> > > >  >>>>>>>> Sprinklerforum mailing list  >>>>>>>>
> > > > [email protected]
> > > >  >>>>>>>>
> > > >  >>>>>>>>
> > > >  >>>>>>>
> > > > >>>>>
> >  > > >>>
> > > >
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > > kl
> >  > er.org
> > > > >>>>>>>>
> > >  > >>>>>>>
> > > >  >>>>>>>
> > > >  >>>>>>>
> > > > >>>>>>>  --
> > > > >>>>>>> Ron Greenman
> > >  > >>>>>>> Instructor
> > > >  >>>>>>> Fire Protection Engineering Technology Bates  Technical
> > > > >>>>>>> College
> > >  > >>>>>>> 1101 So. Yakima Ave.
> > > >  >>>>>>> Tacoma, WA 98405
> > > >  >>>>>>>
> > > > >>>>>>>  [email protected]
> > > > >>>>>>>
> >  > > >>>>>>>  http://www.bates.ctc.edu/fireprotection/
> > > >  >>>>>>>
> > > > >>>>>>>  253.680.7346
> > > > >>>>>>> 253.576.9700  (cell)
> > > > >>>>>>>
> > > >  >>>>>>> Member:
> > > >  >>>>>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS,  WSAFM,
> > > > WFC,
> > > > >>>>>>> WFSC
> > >  > >>>>>>>
> > > >  >>>>>>> They are happy men whose natures sort with their  vocations.
> > > > -Francis
> > > > >>>>>  Bacon,
> > > > >>>>>>> essayist, philosopher,  and statesman (1561-1626)
> > > > >>>>>>> _______________________________________________
> > > >  >>>>>>> Sprinklerforum mailing list  >>>>>>>
> > > > [email protected]
> >  > > >>>>>>>
> > > >  >>>>>>>
> > > > >>>>>
> >  > > >>>
> > > >
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > > kl
> >  > er.org
> > > > >>>>>>>  _______________________________________________
> > > >  >>>>>>> Sprinklerforum mailing list  >>>>>>>
> > > > [email protected]
> >  > > >>>>>>>
> > > >  >>>>>>>
> > > > >>>>>
> >  > > >>>
> > > >
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > > kl
> >  > er.org
> > > > >>>>>>>
> > > >  >>>>>>
> > > > >>>>>>
> >  > > >>>>>>
> > > > >>>>>>  --
> > > > >>>>>> Ron Greenman
> > > >  >>>>>> Instructor
> > > > >>>>>>  Fire Protection Engineering Technology Bates Technical
> > > >  >>>>>> College
> > > > >>>>>>  1101 So. Yakima Ave.
> > > > >>>>>> Tacoma, WA  98405
> > > > >>>>>>
> > > >  >>>>>> [email protected]
> > > >  >>>>>>
> > > > >>>>>>  http://www.bates.ctc.edu/fireprotection/
> > > >  >>>>>>
> > > > >>>>>>  253.680.7346
> > > > >>>>>> 253.576.9700  (cell)
> > > > >>>>>>
> > > >  >>>>>> Member:
> > > > >>>>>>  ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM,
> > > > >>>>>> WFC,
> > > >  >>>>>> WFSC
> > > >  >>>>>>
> > > > >>>>>> They are  happy men whose natures sort with their vocations.
> > >  -Francis
> > > > >>>>> Bacon,
> > > >  >>>>>> essayist, philosopher, and statesman  (1561-1626)
> > > > >>>>>>  _______________________________________________
> > > >  >>>>>> Sprinklerforum mailing list  >>>>>>
> > > > [email protected]
> > >  > >>>>>>
> > > > >>>>>
> >  > > >>>
> > > >
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > > kl
> >  > er.org
> > > > >>>>>  _______________________________________________
> > > >  >>>>> Sprinklerforum mailing list  >>>>>
> > > > [email protected]
> > > >  >>>>>
> > > > >>>>>
> > > >  >>>
> > > >
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > > kl
> >  > er.org
> > > > >>>>>
> > > >  >>>>
> > > > >>>>
> > > >  >>>>
> > > > >>>> --
> > > >  >>>> Ron Greenman
> > > > >>>>  Instructor
> > > > >>>> Fire Protection Engineering  Technology Bates Technical
> > > > >>>> College
> > > > >>>> 1101 So.  Yakima Ave.
> > > > >>>> Tacoma, WA 98405
> > >  > >>>>
> > > > >>>>  [email protected]
> > > > >>>>
> > > >  >>>> http://www.bates.ctc.edu/fireprotection/
> > > >  >>>>
> > > > >>>> 253.680.7346
> > >  > >>>> 253.576.9700 (cell)
> > > >  >>>>
> > > > >>>> Member:
> > > >  >>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM,
> > > > WFC,
> > > > >>>> WFSC
> > > >  >>>>
> > > > >>>> They are happy men whose  natures sort with their vocations.
> > > > >>>>  -Francis
> > > > >>> Bacon,
> > > >  >>>> essayist, philosopher, and statesman (1561-1626)
> > >  > >>>> _______________________________________________
> >  > > >>>> Sprinklerforum mailing list
> > > >  >>>> [email protected]
> > > >  >>>>
> > > > >>>
> > > >
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > > kl
> >  > er.org
> > > > >>>  _______________________________________________
> > > > >>>  Sprinklerforum mailing list
> > > > >>>  [email protected]
> > > > >>>
> >  > > >>>
> > > >
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > > kl
> >  > er.org
> > > > >>>
> > > > >>
> >  > > >>
> > > > >>
> > > > >>  --
> > > > >> Ron Greenman
> > > > >>  Instructor
> > > > >> Fire Protection Engineering Technology  Bates Technical College
> > > > >> 1101 So. Yakima  Ave.
> > > > >> Tacoma, WA 98405
> > > >  >>
> > > > >> [email protected]
> > > >  >>
> > > > >>  http://www.bates.ctc.edu/fireprotection/
> > > > >>
> >  > > >> 253.680.7346
> > > > >> 253.576.9700  (cell)
> > > > >>
> > > > >> Member:
> >  > > >> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM,  WFC,
> > WFSC
> > > > >>
> > > > >> They are happy  men whose natures sort with their vocations.
> > > > >>  -Francis
> > > > Bacon,
> > > > >> essayist,  philosopher, and statesman (1561-1626)
> > > > >> _______________________________________________
> > > > >>  Sprinklerforum mailing list
> > > > >>  [email protected]
> > > > >>
> > >  >
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > > kl
> >  > er.org
> > > > >  _______________________________________________
> > > > >  Sprinklerforum mailing list
> > > > >  [email protected]
> > > > >
> > >  >
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > > kl
> >  > er.org
> > > > >  _______________________________________________
> > > > >  Sprinklerforum mailing list
> > > > >  [email protected]
> > > > >
> > >  >
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > > kl
> >  > er.org
> > > > >  _______________________________________________
> > > > >  Sprinklerforum mailing list
> > > > >  [email protected]
> > > > >
> > >  >
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > > kl
> >  > er.org
> > > >
> > > >  _______________________________________________
> > > >  Sprinklerforum mailing list
> > > >  [email protected]
> > > >
> > >  >
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > > kl
> >  > er.org
> > > >
> > >
> > >
> > >
> >  > --
> > > Ron Greenman
> > > Instructor
> > > Fire  Protection Engineering Technology Bates Technical College
> > > 1101  So. Yakima Ave.
> > > Tacoma, WA 98405
> > >
> > >  [email protected]
> > >
> > >  http://www.bates.ctc.edu/fireprotection/
> > >
> > >  253.680.7346
> > > 253.576.9700 (cell)
> > >
> > >  Member:
> > > ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM,  WFC, WFSC
> > >
> > > They are happy men whose natures sort with  their vocations.
> > > -Francis Bacon, essayist, philosopher, and  statesman (1561-1626)
> > > _______________________________________________
> > > Sprinklerforum  mailing list
> > > [email protected]
> >  >
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > > kl
> >  > er.org
> > >
> >
> >
> >
> > --
> > Greg  McGahan
> > Living Water Fire Protection, LLC  <http://www.livingwaterfp.com>
> > 1160 McKenzie Road
> >  Cantonment, FL 32533
> > 850-937-1850
> > fax 850-937-1852
> >  _______________________________________________
> > Sprinklerforum mailing  list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
> >  rg
> > _______________________________________________
> >  Sprinklerforum mailing list
> >  [email protected]
> >
> >
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
>
>
>
> --
> Greg McGahan
> Living Water Fire Protection, LLC  <http://www.livingwaterfp.com>
> 1160 McKenzie Road
> Cantonment, FL  32533
> 850-937-1850
> fax  850-937-1852
> _______________________________________________
> Sprinklerforum  mailing  list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please visit 
> http://www.symanteccloud.com______________________________________________________________________
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________