Todd,  I had to think about this one awhile.  When I was with the Fire Marshals 
office in Phoenix, we (the City of Phoenix) built two waste recycling, sorting 
and transfer stations.  As I recall, the design density was 0.25 gpm/ft2 over 
2500 ft2.  Looking at the Figures in NFPA 13, for piled storage protection, 
that puts it smack in the middle of the Class IV curve using high temperature 
sprinklers at 20 feet high storage.  That pretty much agrees with Mr. Sornsins 
recollections for his facility, and it is a design that I was comfortable with.

Dwight




________________________________
 From: "Mark A. Sornsin, P.E." <[email protected]>
To: "[email protected]" 
<[email protected]> 
Sent: Friday, August 9, 2013 10:44 AM
Subject: RE: Trash Transfer Station
 

Despite recycling efforts, municipal waste (I think) remains largely paper with 
wood and plastics interspersed. I would expect fires in transfers station piles 
to behave similarly to baled waste paper fires, with added heat release from 
the plastics.

On a facility like this a number of years back, we married the requirements of 
FM data Sheet 8-22 on baled waste paper storage with the requirements of class 
IV solid pile storage (or maybe we used plastics?). Can't recall the details, 
as they were left behind at a previous employer - but that was the concept.


Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd 
Williams
Sent: Friday, August 09, 2013 8:28 AM
To: [email protected]
Subject: Re: Trash Transfer Station

That was my initiating and there was no conclusion posted. In my case I had a 
cascading pile about 12-15 ft high of Class IV (based on observation from 
existing facility). I was considering adjusting the requirements for a pile of 
wood chips (Class III) to Class IV.

>From a letter I received off Forum, supposedly AFSA has information on loss 
>history, but I haven't been able to get a hold of it.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080
www.fpdc.com


On Aug 9, 2013, at 8:31 AM, "Fire Protection Services" 
<[email protected]> wrote:

> Forum
>
>
>
> A few weeks ago there was a post on trash transfer stations.
>
> Could someone tell me what the conclusion was? EH2 comes to mind but
> not sure.
>
> I have deleted those emails and apparently the monthly email to search
> the archives.
>
>
>
> Thanks!
>
>
>
> Chris
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to