How does this happen?  Is the piv not monitored?  Close valve,  receive
trouble at panel. Open valve,  clear trouble. Move on. Simple right?
On Aug 10, 2013 1:31 PM, "Tom Duross" <[email protected]> wrote:

> Oops..   typo.
> Yes, and also would like to share the cause or the organic storage (also
> barged to composting facility in NJ) building burning to the ground this
> past spring.  Unofficially told that the testing company left the isolation
> piv closed that feeds that building.  Still in litigation.  Couldn't get
> in,
> very curious as to what hazard they used.
> TD
>
> Tom,
>
> Just a clarification...I assume you mean to type 0.60/2000.  And the
> placard
> indicated they were using an adjustment for a dry system, which in my book
> is a 30% design areas increase, bringing the system design to 0.60/2600
> ft2.  Of course the pump wasn't designed for this, or even the 0.60/2000,
> but was certainly adequate to control the fire that occurred with 8 heads
> operating at a minimum of 60 gpm.
>
> I think that it would be useful to capture actual system performance in
> these challenging storage fires, to provide feedback to the protection
> committee.
>
> Dwight
>
>
>
>
>
>